Is that a code or local requirement?Do not forget to add a jumper from the cold waterlines to the hot waterlines. I do this at the hot water tank.
Is that a code or local requirement?Do not forget to add a jumper from the cold waterlines to the hot waterlines. I do this at the hot water tank.
Also remember that connections to showers and the such cannot be verified on the final.
Is that a code or local requirement?
Sure they can be, put a meter between the hot and cold, if you have continuity there is noting to bond or look at.
Let me ask this. Where did they come up with the term "Likely to be energised" from for the water lines? Was it due to the fact the lines were connected to a water heater that could short out? To me the word "likely" would infer there was a real good chance of something happening.
Here in Los Angeles inspectors have been requiring me to bond the hot-cold at the water heater for years. We have no local amendment that requires this. The conversation goes like this:
INSPECTOR: "Ah, not so fast there, Sparky, you're gonna need to bond the water heater"
RH1: "Can you show me the code requirement for that?"
INSPECTOR: "I don't have to, I'm telling you to do it"
RH1: "Are you a Code Enforcement Official?"
INSPECTOR: "Yes I am"
RH1: "You enforce building codes?"
INSPECTOR: "Yes I do"
RH1: "Which code are you enforcing right now?"
INSPECTOR: "Look, if you want to take it up with the Chief, you can, but it will delay your job a week"
RH1: "OK, You win, I'll bond the water heater"
Yes. Teflon tape on fittings. Pipe dope. Pex supply lines from shut offs to a faucet.
Also remember that connections to showers and the such cannot be verified on the final.
.
Here in Los Angeles inspectors have been requiring me to bond the hot-cold at the water heater for years. We have no local amendment that requires this. The conversation goes like this:
INSPECTOR: "Ah, not so fast there, Sparky, you're gonna need to bond the water heater"
RH1: "Can you show me the code requirement for that?"
INSPECTOR: "I don't have to, I'm telling you to do it"
RH1: "Are you a Code Enforcement Official?"
INSPECTOR: "Yes I am"
RH1: "You enforce building codes?"
INSPECTOR: "Yes I do"
RH1: "Which code are you enforcing right now?"
INSPECTOR: "Look, if you want to take it up with the Chief, you can, but it will delay your job a week"
RH1: "OK, You win, I'll bond the water heater"
So do you bond every peice of threaded gas pipe if you think it's likely to become energized? By your own view each and every piece and fitting is insulated from each other.
This is getting silly.
There is NO specfic code requirement that requires you to bond between the hot and cold water pipes. Under certain rare circumstances you may find that you have to but in the overwhelming majority of cases you don't.
If you are concerned about shower connections look on the rough. There are tons of things that can't be verified on a final inspection. That doesn't mean they don't exist.
5-235 Log #1834 NEC-P05 Final Action: Reject
(250.104(A)(1))
____________________________________________________________
Submitter: Mark T. Rochon, Mark J. Rochon Master Electrician
Recommendation: Revise as follows:
General Combination metal water piping system(s) separated by nonmetallic
water piping system(s) where may become energized installed in or attached to
a building or structure shall be bonded to the service equipment enclosure, the
grounded conductor at the service, the grounding electrode conductor where of
sufficient size, or the one or more grounding electrodes used.
Substantiation: Nonmetallic water piping systems are being inserted between
our metal water piping system and today?s code is not recognizing these
changes.
Panel Meeting Action: Reject
Panel Statement: The conditions indicated in the substantiation are already
covered by 250.104(B) where there is not a complete metallic water piping
system.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15
____________________________________________________________
5-236 Log #2432 NEC-P05 Final Action: Reject
(250.104(A)(1))
____________________________________________________________
Submitter: Robert P. McGann, City of Cambridge
Recommendation: Revise text to read as follows:
Metal water piping system(s) that is likely to be energized , installed in or
attached to a building or structure shall be bonded.
Substantiation: With much expanded use of plastic water piping system(s)
isolating section of metal piping systems. This type of installation leaves
contractors and inspectors what is required to be bonded.
Panel Meeting Action: Reject
Panel Statement: The requirements of 250.104(A) apply to complete metallic
water piping systems. Where there is no complete metallic water piping
system, then the requirements of 250.104(B) would apply for those portions of
isolated metal water piping system likely to become energized.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15
____________________________________________________________
Forget about my opinions. And sometimes I am silly.
What about the opinions from the NFPA, in the handbook, and the IAEI in the Soares PP that I referenced before?
What are your views on their opinions?
Forget about my opinions. And sometimes I am silly.
What about the opinions from the NFPA, in the handbook, and the IAEI in the Soares PP that I referenced before?
What are your views on their opinions?
unenforceable NEC handbook commentary said:Where it can not be reasonably concluded that the hot and cold water pipes are reliably bonded through mechanical connections, an electrical bonding jumper is required to assure this connection is made.
I also find this much to do about nothing considering the CMPs stance about water pipe bonding.
We will continue to disagree.
Using your logic the gasline is bonded because it is connected to the hot water tank and the tank is connected to the waterlines.
"I think bonding at the water heater harkens back to when the water piping system was required to be electrically continuous"
I hate to read anything into someone else's post. Are you saying that it should or should not be continuous?
Should the copper plumbing be grounded in a residential situation where the main water pipe comes in plastic. ? Lets say the main water comes in plastic, it then changes over to copper right after entering the dwelling and its a new house, for the service 2 grounds were installed, with less than 25ohms of resistance. Should the copper plumbing be grounded so it can never become energized?