Mike you lost me.
Say I just wired a single family dwelling, it is stick built from wood and all domestic water lines are copper including the supply from the water dept.
I have used a uffer and the water line as my grounding electrode system.
It has a an electric hot water heater but I have not installed a bonding jumper from the cold to hot lines at this water heater.
Do I pass or get a red tag from you?
Please cite the NEC section on the red tag.
There is nothing in 90.1 that applies to the above question.
?There is nothing in 90.1 that applies to the above question.?
It applies to everything. It is the purpose of the code. It is the first statement in the code. Why do you think that it is first?
Yes you would fail. 250.104(B). And it does not have to be bonded ?at? the hot water tank.
(A) First I do not think that the cold or hot waterlines need to be bonded at all. Why? If they were properly installed they are NOT likely to be energized. Just MHO.
(B) But we all know that the industry, everyone in the trade, bonds the cold waterlines. Same as we ?jumper? the water meter. No code requirement for jumping the water meter.
So if you objected to my failing (red tag) you, here is how it would play out.
1. As the ESI (Electrical Safety Inspector) I would ask my RBO (Residential Building Official) the AHJ. (I am a RBO)
2. Next he would ask the RPI (Residential Plumbing Inspector), are the cold and hot water pipes different systems? (I am a RPI)
3. The RPI would say yes because there is no requirement to have a hot water piping system. Just hot water.
4. The RPI would use Chapter 607 of the plumbing code to prove the hot water pipes (lines) are a separate system.
5. The RBO would make a decision.
6. The RBO would tell me to treat these as separate systems.
7. Then I would explain to you that ?all? other metal piping ?shall? be bonded.
End of story. Yes you have a right to appeal but I doubt if you could rebut, and win on, my opinions.