No this in not an opinion but the findings of the Code Making Panel charged with the responsibility of writing this section of the code.Mike W. This is an opinion. I have to read what is in the code.
5-236 Log #2432 NEC-P05 Final Action: Reject
(250.104(A)(1))
____________________________________________________________
Submitter: Robert P. McGann, City of Cambridge
Recommendation: Revise text to read as follows:
Metal water piping system(s) that is likely to be energized , installed in or attached to a building or structure shall be bonded.
Substantiation: With much expanded use of plastic water piping system(s) isolating section of metal piping systems. This type of installation leaves contractors and inspectors what is required to be bonded.
Panel Meeting Action: Reject
Panel Statement: The requirements of 250.104(A) apply to complete metallic water piping systems. Where there is no complete metallic water piping system, then the requirements of 250.104(B) would apply for those portions of isolated metal water piping system likely to become energized.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15
.
And what part of Article 90 is enforceable? None of it! It is the introduction to the code and not one word found therein can be enforced in the field. It clearly states that any electrical installation made in compliance with this code would be a safe installation. It does not say that any electrical installation made in compliance with this and all the other codes.Read 90.1(C) BTW I am NOT saying that you are untrained. It just says that this is not an instruction manual. It contains rules reguarding electrical connections.
No sir we do not agree that other codes are used by the electrician. Should you turn down my electrical installation due to the lack of smoke alarms you would be required in the state of NC to show me where smoke alarms are required in the NC Electrical Code. This would cause you a trip to the Qualification Board that issued you your inspector?s certificate.So we agree that other codes are use by an electrician. And yes I could turn you down for no smokes. Because you are not ready for an electrical inspection. I am required to inspect the wiring of smoke detectors. If they are not present I can not inspect them. For the same reason I could fail you for them not being AFCI protected on the final. No I could not fail you for the placement of them.
Remember it was you that said; ?I would only use the NEC for an electrical inspection? and there is no where in the electrical code that requires a smoke alarm therefore you would have nothing to use for the rejection.
What part of 250.4(A)(4 & 5) have to do with bonding the hot and cold water pipes together? I don?t see anything in those sections that address the metal water pipe. The metal water pipe is addressed in 250.104.Just because you get continuity with a wiggy does not meet 250.4(A)(4 & 5)
Personally I would use some sort of multi-meter to test the continuity but if I didn?t get a reading then it wouldn?t be a complete metal water pipe would it? Now I fall back to 250.104(B) as outlined by the Panel Statement above.
Now if you would be so kind please answer the question I asked in this post