Also, 406.4(D) was cited. Consider:
2014 NEC
406.4(D)(1) Grounding-Type Receptacles. Where a grounding means exists in the receptacle enclosure or an equipment grounding conductor is installed in accordance with 250.130(C), grounding-type receptacles shall be used and shall be connected to the equipment grounding conductor in accordance with 406.4(C) or 250.130(C).
We can't use the rule 250.130(C) because it is limited to ungrounded wiring methods. So let's go to 406.4(C):
2014 NEC
406.4(C) Methods of Grounding. The equipment grounding conductor contacts of receptacles and cord connectors shall be grounded by connection to the equipment grounding conductor of the circuit supplying the receptacle or cord connector.
(info note about electrical noise)
The branch-circuit wiring method shall include or provide an equipment grounding conductor to which the equipment grounding conductor contacts of the receptacle or cord connector are connected.
(info note #1: See 250.118 for acceptable grounding means.)
(info note #2: leads to 250.130 which doesn't apply)
So, going to 250.118, let's go straight to 250.118(8):
2014 NEC
250.118 Types of Equipment Grounding Conductors.
(8) Armor of Type AC cable as provided in 320.108.
Period. That is ALL (8) contains. I'm not omitting anything.
So, going to 320.108:
2014 NEC
320.108 Equipment Grounding Conductor. Type AC cable shall provide an adequate path for fault current as required by 250.4(A)(5) or (B)(4) to act as an equipment grounding conductor.
And we seem to be in a cul-de-sac that has no other meaning. But I submit that there is a single clear fork in the trail that was missed back in 406.4(D)(1).
Now, please, bear with me. As I have said from the beginning, the difficulty, in our discussion here in this thread, is the assumption that AC type BX is ungrounded. To follow my logic, my reading of the Holy Writ, allow that type BX is grandfathered as an "existing grounding means" and keep that in mind to the bottom of this post.
406.4(D)(1) contains two very different things: 1) a receptacle enclosure with an EXISTING grounding means; or 2) the INSTALLATION of an EGC by 250.130(C).
No new EGC (in the wiring method) is going to be installed so 250.130(C) doesn't apply as it is limited in the first paragraph of 250.130 to ungrounded wiring methods (please, bear with me).
So we go to 406.4(C) and the first sentence tells us to bond from the receptacle device to the EGC of the supplying circuit. Looking at the related Informational Note we see noise reduction guidance.
At this point, and this is the heart of my position, NOTHING is said that defines the nature of the "existing grounding means." That information is in SEPARATE informational notes that append to the second sentence of 406.4(C). Observe that the numbering of the informational notes RESTARTS after the second sentence.
In a receptacle replacement in a box supplied by AC type BX, no new branch-circuit wiring is installed . . . and that is what the second sentence of 406.4(C) is about, a newly installed branch-circuit wiring method. So the second sentence doesn't come into play, and we never get to the informational notes for the second sentence.
Thank you for bearing with me as you read this. I maintain that the
Code is silent about an existing wired to the
Code of its original install AC type BX cable as a grounding means, which means the EGC is still there.