Actually, it's about the linguistics of code-reading
Actually, it's about the linguistics of code-reading
I argued that 250.130(C) demands that, when replacing a non-grounding receptacle with a grounding one, you must have a modern EGC . But Al quoted the section below, arguing that 250.130(C) applies only when there's no EGC in the circuit, per the text in red. Since the BX was accepted, back in the day, as an EGC, he asserts that 250.130(C) doesn't apply. Take a look:
That sentence is ambiguous. Al is, in good faith, interpreting it differently than I am:
Al's reading:
(For replacement {of non–grounding-type receptacles with grounding-type receptacles and for branch circuit extensions}
only in existing installations that do not have an equipment grounding conductor in the branch circuit,)
(connections shall be permitted as indicated in 250.130(C).)
In other words, (C) applies -- to the receptacle replacement and to the branch-circuit extensions -- but only if there's no EGC.
My reading:
(For replacement of {non–grounding-type receptacles with grounding-type receptacles}
and {for branch circuit extensions only in existing installations that do not have an equipment grounding conductor in the branch circuit,}
(connections shall be permitted as indicated in 250.130(C).)
In other words, (C) applies to the receptacle replacement. And it also applies to those branch-circuit extensions that lack an EGC.
I am confident that my interpretation is the intended one. But my goal with this post is only to show the ambiguity that's leading to Al's disregard for 250.130(C), while I think it settles the matter.
Actually, it's about the linguistics of code-reading
I argued that 250.130(C) demands that, when replacing a non-grounding receptacle with a grounding one, you must have a modern EGC . But Al quoted the section below, arguing that 250.130(C) applies only when there's no EGC in the circuit, per the text in red. Since the BX was accepted, back in the day, as an EGC, he asserts that 250.130(C) doesn't apply. Take a look:
In using 250.130(C) to substantiate your claim, you have overlooked the first part of that Rule:VII. Methods of Equipment Grounding
250.130 Equipment Grounding Conductor Connections. [...] For replacement of non–grounding-type receptacles with grounding-type receptacles and for branch circuit extensions only in existing installations that do not have an equipment grounding conductor in the branch circuit, connections shall be permitted as indicated in 250.130(C).
That sentence is ambiguous. Al is, in good faith, interpreting it differently than I am:
Al's reading:
(For replacement {of non–grounding-type receptacles with grounding-type receptacles and for branch circuit extensions}
only in existing installations that do not have an equipment grounding conductor in the branch circuit,)
(connections shall be permitted as indicated in 250.130(C).)
In other words, (C) applies -- to the receptacle replacement and to the branch-circuit extensions -- but only if there's no EGC.
My reading:
(For replacement of {non–grounding-type receptacles with grounding-type receptacles}
and {for branch circuit extensions only in existing installations that do not have an equipment grounding conductor in the branch circuit,}
(connections shall be permitted as indicated in 250.130(C).)
In other words, (C) applies to the receptacle replacement. And it also applies to those branch-circuit extensions that lack an EGC.
I am confident that my interpretation is the intended one. But my goal with this post is only to show the ambiguity that's leading to Al's disregard for 250.130(C), while I think it settles the matter.