Yes, that is what I said. The code references were to point out ways one could put in three wire recpts without replacing the existing wiring. Alternately one could use two wire recpts.Could someone answer a question for me. Action Dave said in the first post to the op if the bx had no bond strip it couldn't be used for a ground. Is that right? I have done hundreds of jobs, service changes, etc, where there was no bond strip in the bx. You strip some it has paper to peel off. Some has waxed cloth to get off. No inspector (and some very knowledgeable) has ever questioned or mentioned the age or acceptability of this bx.
Am I missing something?
Is there bx after the 1960 date with no bond strip that is ok?
Are some saying all these systems should considered ungrounded?
Nobody is arguing that old BX has to be ripped out, just whether or not the sheathe is an acceptable EGC. Al is as sharp as anybody on this forum. Most of the time I agree with him. In this case I do not.
Type AC cable since 1960 something includes the bonding strip that makes the sheathe suitable for an EGC.