al hildenbrand
- Minnesota
- Electrical Contractor, Electrical Consultant, Electrical Engineer
Folks, thanks for the continued discussion of this aspect of the NEC. I am still, in this thread, endeavoring to constrain my comments to the Code itself. Opinion with Code citation is helpful.
"Grandfathering" is a challenging conversation, as we are experiencing. Armored Cable type BX (non-bonding strip) that was installed as a "system" has been required by Code to be grounded and has been a "grounding means" for at least a Century, as I have shown in the 1918 NEC quotes in an earlier post in this thread.
I am trying to understand how that status of being a grounding means is reversed to NOT being a grounding means by newer editions of the NEC.
A lot of weight, in this thread, is being given to whether grounding-type receptacle devices were used in type BX Armored Cable wiring method systems. . . . and, with this morning's coffee, I came to a thought about a parallel in real-world wiring in dwellings and occupancies.
Please consider a receptacle device replacement in an occupancy built in the early 1970s with Flexible Metal Conduit (FMC) as the primary wiring method. I live and work in a Metro Area of nearly 3 million souls. In it, there are tens of thousands of dwellings built since the 1962 NEC went into effect requiring ALL receptacle outlets to be of the grounding type, and before LOCAL ordinance, requiring ALL-METAL wiring methods only, was relaxed to also allow nonmetallic wiring methods.
Lets narrow this consideration to an early 1970s 120 Volt 15 Amp branch circuit wired to the Code of its original installation (early 1970s) wired with FMC (flexible metal conduit) and all associated metal fittings and boxes, with the actual wire being TW solid copper #14 gauge HOT and NEUTRAL only - (the FMC itself is the entire EGC per early 1970s NEC - there is NO equipment grounding #14 gauge copper wire inside the FMC).
To replace an existing duplex grounding-type receptacle device in an existing receptacle outlet in this early 1970s FMC branch circuit where only the FMC is the "existing grounding means", do YOU treat the FMC as an ungrounded wiring method?