Forgive me for the length. We are in the center of the matter, finally.
250.130(C) does demand an EGC, and its the Article 100 definition of EGC that references 250.118
So you are pointed toward 250.118, but you are taking the long way there.
In the opening of the rule 250.130 last sentence that guides us to 250.130(C), I'm not finding the instructions to install an EGC (2014 defined) nor am I finding the instructions to use only an EGC as defined by today's
Code, which you, as you are reading it, seem to be finding.
This is interesting. Somehow the NEC terminates the "grandfathered" installed to the
Code of its original installation status as a "grounding means" of two different wiring methods -- 1.) Armored Cable type BX, 2.) Flexible Metal Conduit of over six feet aggregate length.
Armored Cable type BX was manufactured and installed in an era of nongrounding-type receptacles being predominant, however, when required GROUNDING-type receptacles were installed, they were grounded by the device screws attachment to the receptacle outlet box (as was the
Code of that day) because the BX was installed as a grounding means per that day's
Code.
Flexible Metal Conduit (FMC) is also a wiring method that has had its status as an EGC altered as the
Code editions have evolved, although FMC has not had to have its manufacturing altered. The metal of FMC was recognized as a grounding means, regardless of length, until the "6 feet" restriction of the 1971 NEC 250-91(b)
Exception No. 1(a.) appeared for the first time. All receptacle devices installed at that time had to be of the grounding-type, and that had been true since the 1962 NEC was adopted.
Also, parenthetically, note that 1968 NEC Article 100 Definitions has the FIRST appearance of the defined term "Grounding Conductor, Equipment". For the first almost 3/4 century of the NEC, the EGC was NOT called the EGC.
In my work area, there was a housing boom, post WWII, that was in full swing, and an existing local ordinance(s) that prohibited NONmetallic wiring methods like NM. Some areas are almost 100% FMC, others are almost 100% Armored Cable and, depending on date of construction, are either type BX or type AC. Infill new construction, and new additions / remodels will be scattered all over the Metro area and ALL this new construction is matching to the work found in NEW Occupancy ADDITIONS to the Metro Area. (However, if one got out far enough from City Center, the "all-metal" ordinances didn't reach, and NM was the primary wiring method.)
My State has had an Electrical Act at the level of State Wide Statute, with enforcement, since 1899. Yes, EIGHTEEN ninety nine. There are a lot of good minds here. The cognitive dissonance I experience between the certainties in this thread about BX and FMC, and the Real World of my work area outside my door is high.
Somewhere, something is being missed. . . here, this thread, has said I am missing it, that the
Code is clear. OK. Show it to me.
The immediate rejoinder is "look at 250.118." But, Why?
How, in a "receptacle replacement" in an existing outlet that starts in 406.4, does the
Code, not you, or your opinion, does the
Code narrow an existing outlets wiring method's existing grounding means to the choices ONLY in 2014 NEC 250.118?
Netpog, I see your point and agree that the first part of 250.130 reads as follows:
2014 NEC
VII. Methods of Equipment Grounding
250.130 Equipment Grounding Conductor Connections. . . . For replacement of nongrounding-type receptacles with grounding-type receptacles . . . , connections shall be permitted as indicated in 250.130(C).
So, when I am ONLY replacing a receptacle device (that is, I am not installing a NEW branch circuit extension or NEW EGC with the branch circuit conductors) in an existing "outlet" that has an "existing" "conductive(s) path that provides a ground-fault current path and connects normally non-current-carrying metal parts of equipment together and to the system grounded conductor or to the grounding electrode conductor, or both," (Note that this is the Definition of Grounding Conductor, Equipment from Article 100.) I check that "connections" are as "permitted" in 250.130(C).
Bear with me now, I will return to this last sentence, "I check that 'connections' are as 'permitted' in 250.130(C)."
But I have two "or" in the logic tree that leads me to 250.130(C), and they are back in 406.4(D)(1) in that one-sentence-rule.
This is the start of "receptacle replacement" as I see it.
406.4 General Installation Requirements. Receptacle outlets shall be located in branch circuits in accordance with Part III of Article 210. General installation requirements shall be in accordance with 406.4(A) through (F).
(D) Replacements. Replacement of receptacles shall comply with 406.4(D)(1) through (D)(6), as applicable.
(1) Grounding-Type Receptacles. Where a grounding means exists in the receptacle enclosure or an equipment grounding conductor is installed in accordance with 250.130(C), grounding-type receptacles shall be used and shall be connected to the equipment grounding conductor in accordance with 406.4(C) or 250.130(C).
(2) Non–Grounding-Type Receptacles. Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(2)(a), (D)(2)(b), or (D)(2)(c).
I only have to know that a grounding means exists. Earlier
Codes in effect at the time of installation, establish the grounding means existence, at that time.
Because of the first "or" I do not have to look further, I skip EGC (because no new EGC is being installed), and read "shall be connected to the equipment grounding conductor in accordance with 406.4(C)
or 250.130(C)," and I choose 250.130(C). I don't have a choice in this matter about the grounding-type receptacle, even if the existing receptacle device that I am to replace is an nongrounding-type, because I HAVE to use a grounding-type "Where a grounding means exist".
"But" you say, "it says you have to connect to the "equipment grounding conductor" which puts you in 250.118 which, in turn, says BX, or >6' lengths of FMC, are not grounding means. . .
Paradox. We're only at this use of "equipment grounding conductor" because of "Where
a grounding means exists in the receptacle enclosure" . . . The old
Codes unambiguously establish the armor of "armored cable", without restriction, as a grounding means as I have quoted them from 1918 until 1959.
I do have to check that "conductive path(s) that provides a ground-fault current path and connects normally non-current-carrying metal parts of equipment together and to the system grounded conductor or to the grounding electrode conductor, or both," is electrically present at the existing outlet in front of me and at the service center from which it originates and that will satisfy 250.130(C), most likely 250.130(C)(1) or 250.130(C)(5).
And there I have returned us to 250.130(C). We never went to 406.4(C) because of the
"or".
As I have said from the very beginning of this thread, the problem is everybody can't use 250.118 without first arriving at it through the NEC, by which I mean, one can't start by assuming that old non-bonding strip BX was NEVER a grounding means.
The original BX
Code approved installation as a grounding means is preserved until it is removed by the NEC. I've just shown a path through today's 2014 NEC that makes use of that existing older
Code status. I think it is correct. Regardless, if my opinion, where is the
Code cited wrong?