OK, Wayne.Al, maybe I'm being dense, but I still don't see an answer to my questions in that writing of yours that you have repeated several times. So would you please just answer my questions directly, or try rephrasing your point?
The "new construction" in a receptacle replacement at an existing outlet is the receptacle device, some form of bonding (if used) and maybe a coverplate. I first go to 406.4(D). I correlate the receptacle in relationship to the occupancy and apply the parts of 406.4(D) to the choice of the new device I will select to replace the existing device. (Obviously, there can be box volume issues, but let's keep this simple, and say there is enough volume.)
406.4(D) does not guide me in anyway to modify or replace the existing branch circuit wiring method (assuming it is installed to the Code of its inspection and approval). Rather, I am, in 406.4(D)(1) allowed, when there is an existing grounding means, to connect the new required grounding-type receptacle to that equipment grounding conductor.
I am never, by the NEC, instructed to restrict the existing wiring method grounding means to the list only in 250.118.
What I believe is the error, here, is to apply 250.118, before I walk up to the existing receptacle outlet, to a legally installed, existing grounded wiring method of its day, to say that the wiring method was never a grounded wiring method. The NEC is silent about this. If I have some of the old material that is UNinstalled and I wish to install it now, then the rules of the current NEC, as pertains to that new installation, take precedent. But a receptacle replacement in an existing outlet on an existing Branch Circuit is NOT modifying the existing Branch Circuit, it is maintaining the outlet.