This project is for a small ethanol distilling process skid. The actual amount of ethanol in the process is small...a couple of gallons at most. Since ethanol vapor is heavier than air, it would tend to settle near the floor. Also, the pumps for the process are located near the floor. That was the reasoning for the C1D1 classification below 18 inches.
As I mentioned in Post #17, depending on the level of ventilation, this current description appears to be Class I, Division 2 throughout.I forgot to add... The skid will be located in an enclosed space that is ventilated.
Since over-classifiying is not in and of itself a safety issue, it's OK but far more expensive than necessary. (That's why we have Division 2) Introducing explosionproof boundary seals, more restrictive wiring methods and enclosures types below the 18" demarcation will be a big deal.