anybody else have thoughts on this?
why don't you try reading the code book?
Sure, but I thought I'd let you two take it outside and duke it out.anybody else have thoughts on this?
Here we see the method of sealing must surround both the conductors AND the outer jacket.Cables Capable of Transmitting Gases or Vapors.
Cables with a gas/vaportight continuous sheath capable of
transmitting gases or vapors through the cable core, installed
in conduit, shall be sealed in the Class 1, Division 1
location after the jacket and any other coverings have been
removed so that the sealing compound can surround each
individual insulated conductor or optical fiber tube and the
outer jacket.
This is primarily for the benefit of boundary seals to permit them to be treated as a single conductor at the boundary without needing to remove the jacket; however, the same benefit may be achieved at the enclosure IF the outer jacket is included within the overall internal sealing method within the enclosure. In other words, the conductors AND the outer jacket must still be within the same sealing method inside the enclosure. The additional note about shielded. twisted pairs is just an addendum.Exception: Multiconductor cables with a gas/vaportight
continuous sheath capable of transmitting gases or vapors
through the cable core shall be permitted to be considered
as a single conductor by sealing the cable in the conduit
within 450 mm (18 in.) of the enclosure and the cable end
within the enclosure by an approved means to minimize the
entrance of gases or vapors and prevent the propagation of
flame into the cable core, or by other approved methods. It
shall not be required to remove the shielding material or
separate the twisted pairs of shielded cables and twisted
pair cables.
Sure, but I thought I'd let you two take it outside and duke it out.
It's important to recognize an Exception does not necessarily wipe out the main text entirely. From Section 501.15(D)(2) main text:
Here we see the method of sealing must surround both the conductors AND the outer jacket.
From the Exception:
This is primarily for the benefit of boundary seals to permit them to be treated as a single conductor at the boundary without needing to remove the jacket; however, the same benefit may be achieved at the enclosure IF the outer jacket is included within the overall internal sealing method within the enclosure. In other words, the conductors AND the outer jacket must still be within the same sealing method inside the enclosure. The additional note about shielded. twisted pairs is just an addendum.
In the rare case (which I avoid like the plague) where I have had to use multiconductor cable in conduit, I have used a shrinkon sleeve with an internal melting mastic.
As an interesting side note, read the last sentence of Section 501.15(E)(1) for Division 2 applications.
Next question: How do you know you have, "A cable with a gas/vaportight continuous sheath".
Previous discussion and guidance from rbalex.
http://forums.mikeholt.com/showthread.php?t=161925&highlight=+501.15++nhee2
I have not interpreted the approved means in 501.15(D)(1) exception to require TCMX or chico, but that interpretation was influenced by the thread above.
Dale001289 and nhee2 - good work you two. The critical point is the multiconductor cable (in conduit) jacket is sealed in the same "mass" as the conductors at the cable's end. It actually applies even when the multiconductor cable isn't in a conduit - it's just easier to accomplish.
It may also be relevant to know that I use Section 500.8(A)(3) when I'm forced to seal such a cable. I also spend a bit of time with the local AHJ in advance to assure acceptance. I never had a problem.
In addition, while shielded/twisted pairs have their own general exception, the truth is, many multiconductor cables of any Type construction may "gas block" sufficiently on their own in as little as 10 feet. But neither UL nor the manufacturers are willing to state just what that minimum length may be for any given cable construction/installation. There are just too many variables. SO - I just say forget Sections 501.15(D)(3) and E(2) since they only apply to Type MI and it has its own specific installation rules anyway [Section 501.10(A)(1)(b)]. Section 501.15(E)(2) does have some value since it describes the acceptable "leak rate". (IMO that should be in somewhere in Section 501.15(C), but that's just my opinion.)
The critical point is the multiconductor cable (in conduit) jacket is sealed in the same "mass" as the conductors at the cable's end. It actually applies even when the multiconductor cable isn't in a conduit - it's just easier to accomplish.
Sorry I confused you. I still couldn't find the illustration I mentioned four years ago. I've attached two pictures I hope will help.I'm confused by this statement - what are you considering the 'mass'? Mass of sealant?
For an explosion-proof transmitter with a twisted shielded pair - I interpret this can be an EY type seal fitting with cable and chico (no stripping of insulation), with cable continuing through < 18" of conduit/fittings to the transmitter. Cable jacket stripped at transmitter, and heat shrink the cable ends with adhesive backed heat shrink (assuming the AHJ 'approves'). Is this consistent with what you are saying?
i asked the manufacturer (usually Belden) they confirmedNext question: How do you know you have, "A cable with a gas/vaportight continuous sheath".
This is primarily for the benefit of boundary seals to permit them to be treated as a single conductor at the boundary without needing to remove the jacket; however, the same benefit may be achieved at the enclosure IF the outer jacket is included within the overall internal sealing method within the enclosure. In other words, the conductors AND the outer jacket must still be within the same sealing method inside the enclosure. The additional note about shielded. twisted pairs is just an addendum.
I prefer Dale001189's answer, but yours is fine.i asked the manufacturer (usually Belden) they confirmed
I’d advise you to do the same. According to you anything the AHJ happens to like - tape, cold shrink etc could be “approved” - the seal
Has to block gases from entering the internal part of the cable -
Sent from my iPhone using Tapatalk
Absolutely correct, which was the original reason for the general instrument cable exception. Of course most shields are Mylar backed and basically insulated.the problem i see with removing jacket at seal offs is when you have shielded cable, chico seal is cement and when wet semi conductive, you just double bonded your shield.
Google Adhesive Lined Heat Shrink Tubing; there are plenty of sources.when tsc is used not in a seal-off, the compound surrounds every conductor and the jacket, it wouldn't make sense to me if you only surrounded the conductors and didn't seal the inside of the jacket
do you know what melting seal you are referring to (even brand name guess)
TSC is listed for explosion-proof seals
and no seal completely seals out gases, all of them only minimize
why the h*** do you think the code allows this?
Google Adhesive Lined Heat Shrink Tubing; there are plenty of sources.
Absolutely correct, which was the original reason for the general instrument cable exception. Of course most shields are Mylar backed and basically insulated.