Try 3M EPS-300.im just finding normal heat shrink, do you use standard heat shrink and melt them together? i took it there was something designed specifically for the use
Try 3M EPS-300.im just finding normal heat shrink, do you use standard heat shrink and melt them together? i took it there was something designed specifically for the use
Bob
.I also recall, MI cable - which is rarely used for power applications - is considered to be the only true gas/vapor blocked cable available.
MMMMMmmmmmm…. not too likely. For the moment UL won't even certify that Type UF (Art 340) even has a "gas/vaportight continuous sheath" although it probably does. But, for the record, See Section 340.12(7).we sometimes use a cable that has a sheath that is molded around the conductors which falls under that, i think uf is like that ain't it?
i don't believe UF would be certified for that i was just using that as a reference for the molded sheath. i should've been more clear. i have seen cables that say incapable of transmitting on spec sheets. i was asking if uf had molded sheath i think it does, i don't remember for sure though, i barely ever see itMMMMMmmmmmm…. not too likely. For the moment UL won't even certify that Type UF (Art 340) even has a "gas/vaportight continuous sheath" although it probably does. But, for the record, See Section 340.12(7).
As of right now, UL does not have a standard to certify any non-MI cable construction to be incapable of transmitting gases or vapors through the core. This is primarily because the MI fittings listed for the location already seal it. [Section 501.10(A)(1)(b)] So what you have seen in "spec sheets" is essentially marketing material. Get a copy of the UL White Book and compare a manufacturer's sales literature against the UL Category Code. You can also do this with the UL Online Certification Directory.i don't believe UF would be certified for that i was just using that as a reference for the molded sheath. i should've been more clear. i have seen cables that say incapable of transmitting on spec sheets. i was asking if uf had molded sheath i think it does, i don't remember for sure though, i barely ever see it
As of right now, UL does not have a standard to certify any non-MI cable construction to be incapable of transmitting gases or vapors through the core. This is primarily because the MI fittings listed for the location already seal it. [Section 501.10(A)(1)(b)] So what you have seen in "spec sheets" is essentially marketing material. Get a copy of the UL White Book and compare a manufacturer's sales literature against the UL Category Code. You can also do this with the UL Online Certification Directory.
You should still have a copy of the White Book anyway. It has a wealth of application material, it's free and basically a good start for checking conformance with Section 110.3(B). It also has information beyond the UL Online Certification Directory.
As I mentioned before, several cable constructions are capable of passing the "leak test" [[200 cm3/hr (0.007 ft~/hr) of air at a pressure of 1500 pascals (6 in. of water)] from length alone. However, any differential pressure even marginally above that makes an installation immediately suspect. As it presently stands, neither UL nor any reputable manufacturer has a verifiable documented standard for consistently testing gas blocking under all installation conditions. There are just too many variables to consider.you probably won't believe me but i actually have a white book. i don't have my code book on me right now though, does that cable have to be listed as incapable of transmitting gases? i will look on free access right now but i don't trust myself coming to conclusion by looking on there, it just takes too long to flip back and forth
501.15(D)(3)
is there somewhere that requires the listing
thanks for the ul online directory, i didn't know about that
BTW, the insulation never needs to be removed, only the jacket and/or sheath. In fact, the cement type sealing material is slightly conductive.
As I mentioned before, several cable constructions are capable of passing the "leak test" [[200 cm3/hr (0.007 ft~/hr) of air at a pressure of 1500 pascals (6 in. of water)] from length alone. However, any differential pressure even marginally above that makes an installation immediately suspect. As it presently stands, neither UL nor any reputable manufacturer has a verifiable documented standard for consistently testing gas blocking under all installation conditions. There are just too many variables to consider.
As of right now, UL does not have a standard to certify any non-MI cable construction to be incapable of transmitting gases or vapors through the core. This is primarily because the MI fittings listed for the location already seal it. [Section 501.10(A)(1)(b)] So what you have seen in "spec sheets" is essentially marketing material.
Well get your copy of the NEC or look it up here for the cost of registering with the NFPA. You don’t have to become a member.i didn't think non-process seals were required to hold pressure. once again i don't have my code book with me, sorry.
i also don't think the cable has to be listed for that, do you?
all i am talking about is non process seals by the way, just standard c1 d1.
thanks
Well get your copy of the NEC or look it up here for the cost of registering with the NFPA. You don’t have to become a member.
Even non-process seals have a pressure requirement. See Section 501.15(E)(2) and read it carefully.
You are rapidly approaching my minimum consultant fee.
My understanding is the cable manufacturer's have no incentive to pay for a listing and create a new product since they see no market. There are other solutions customers end up using.
do you have a code reference for it having to be listed for that?It would be required by the NEC to be listed to that affect. I would not proceed with construction assuming the AHJ would interpret otherwise, it is a big risk for the project.
I was involved in the early stages of developing Sections 501.15 (D) and (E). It was my suggestion to API to Propose what became MC-HL that set the wheels rolling for a variety of cable applications. Sealing cables was always murky at the time. Depending on who is interpreting it, it may still be.
You would be surprised how many cable manufactures at the time were indeed interested in developing a standard for gas blocked cable. As I said, they dropped it because UL and the manufacturers couldn’t determine a suitable test that could be consistently applied in general.
EDIT ADD: As for a Code reference if you were attempting to apply one of the gas blocked Sections it would fall under Section 110.3(B).