iwire said:
A copper conductor ........... so whats the point?
I really am not into playing 20 questions.
:roll:
crossman said:
You're right. I left out that and was only talking about the rebar since it is the issue at hand. I should have been more thorough.
Okay, my reading of 250.52(A)(3) concenring the cooper wire. The portion of the wire that is embedded in the concrete is the electrode. Anything protruding out of the concrete would then be the GEC...
You agreed with his previous thoroughness that skipped what a CEE is.
&
tryinghard said:
Wow, this is the point I've been pressing.
It is the issue at hand for the 'stubbers' because when the electrician installs this it is compliant and the literal sense of a rebar stub is not compliant.
Who cares what it?s called when it is within 2? of protruding this is no different than connecting onto a rebar stub.
&
iwire said:
I am still not getting it at all.
Well I think I?m on topic, maybe I?m not?? I went on to
resolve the issues of rebar stubs being compliant or non-compliant CEE?s. I advocate the #4cu for the electrode
as the remedy to this rebar problem. You?re pointing to 250.52(A)(3), CEE, and so am I.
iwire said:
In my opinion it is a NEC violation to stub the rebar out of the foundation for connection to the GEC.
This is fact in the truest sense of the code we are deciphering, it is also avoidable by using #4 cu as the electrode and stub it long enough to terminate at the service disconnect, no splice at all for the GEC. The AHJ?s may often determine the rebar/#4cu stubs as electrodes and simply allow the GEC to connect at the stub, but if the #4cu is long enough this is a mute point and if its too short splice it (250.64(C)!
iwire said:
250.52(A)(3) defines what a CEE is. That description requires that the CEE be surrounded by at least 2" of concrete.
The end of the first sentence is the electrode to use to avoid the rebar stub issues, as I stated previously install this electrode point to point to avoid any rebar issues.
iwire said:
Given that definition the rebar that is stubbed out is not a CEE. It is simply a steel conductor attached to the the CEE so in reality the stubbed out section is a GEC.
If you select the #4 electrode it can easily be run long enough to reach its destination, or it can be spliced, NEC does not direct us how to extend rebar stub.
iwire said:
250.62 prohibits using steel as a GEC.
use the #4 cu
iwire said:
In my opinion and due to 250.64(A) the only legal way to connect to a rebar CEE is with a copper conductor connected to the rebar in the area defined by 250.52(A)(3).
unless you use #4cu for both
iwire said:
All you 'stubbers' are in violation of the NEC. :grin:
not me, I stub enough to reach the service disconnect. The real violation is the electrician that assumes the rebar is compliant without checking, this same electrician assumes some inspector will check and the installer cares about proper grounding electrodes, this type of electrician just assumes the electrode.
Maybe I?m too far off topic or maybe not, I?ve been concentrating on the fix.