Mark, excellent graphic, thanks for taking the time to make it and post it.
I was away for a bit and crossman has answered your questions in much the same way as I would have.
If it's not surrounded by concrete it is no longer a concrete encased electrode. That really is not interpretation or opinion, that is a fact found in 250.52(A)(3)
The fact that it could be one long unbroken section of material has nothing to do with it being an CEE or not.
As to your graphic, I would move point 'A' 2" into the concrete. Once that is done everything from 'A' into the cement may well be a CEE. Anything from 'A' to the panel has to be a GEC.
To add - if you stubbed up rebar under a main cabinet and found some (rare) lug rated for connection to steel, strong armed it and applied that to your neutral bar - you would have similarly applied your "electrode" directly to the neutral.
Lets say you did that, per the NEC the 'system' would not be grounded. The NEC requires that the system be grounded by a connecting a GEC to the neutral. 250.24(A).