Someone recently told me that you cannot use a chase nipple with a #4 or larger conductor since the requirement is that the chase nipple would need a insulating bushing on each side.  Anyone ever hear of this?  Here's the relevant section:
	
		
			
		
		
	
				
			300.4(G) Insulated Fittings. Where raceways contain 4 AWG or larger insulated circuit conductors and these conductors enter a cabinet, box, enclosure, or raceway, the conductors shall be protected by a substantial fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by substantial insulating material that is securely fastened in place.
Exception: Where threaded hubs or bosses that are an integral part of a cabinet, box, enclosure, or raceway provide a smoothly rounded or flared entry for conductors.
Conduit bushings constructed wholly of insulating material shall not be used to secure a fitting or raceway. The insulating fitting or insulating material shall have a temperature rating not less than the insulation temperature rating of the installed conductors
 
				
 
 
		 
 
		 
 
		 
 
		 
 
		 
 
		