Dwelling has a 200-amp service with the utility meter outside and the 200-amp main breaker panel inside...SEU 3-wire between outside meter and inside main breaker service equipment.
Now the electrical contractor adds a generator with a SUSE rated 200-amp transfer switch and the installation is arranged according to 230.85(3) with the SUSE rated transfer switch outside adjacent to the meter, with 3-wire SEU load side connected from the SUSE rated 200-amp transfer switch into the existing 200-amp main breaker service equipment inside and Marks the SUSE rated transfer switch with a label according to 230.85(3), EMERGENCY DISCONNECT-NOT SERVICE EQUIPMENT.
This is Code compliant under the 2020 NEC per section 230.82(10) and 230.85(3)
Now when utility power is out and the system runs on generator you have 4-wire Feeder from the generator feeding a 3-wire arranged system.
Now a solar contractor comes and adds a Supply-Side connected PV Interactive System with an ESS that can operate as a Hybrid System. Again connected per 230.82(6) and 230.85(3) and Marks the SUSE rated 690.13 PV System Disconnecting Means with a label according to 230.85(3), EMERGENCY DISCONNECT-NOT SERVICE EQUIPMENT. The system is wired from the Supply-Side connection to the PV System Disconnect with another 3-wire arrangement.
This Dwelling wiring arrangement will have multiple system bonds per 250.24(A)(4), at the existing Service Equipment, the generator transfer switch and the PV System Disconnect. There is still only 1-Service to the Dwelling, but with multiple system bonds required by Code, but against the intent of 250.24(A)(5) creating multiple paths for unbalanced system current and fault current.
I do not consider this a safe arrangement. There should be only 1-system bonding jumper with a 4-wire arrangement (grounded conductor and equipment grounding conductor separate) downstream to all other system interconnections.
You don't see an issue with this?