Re: commercial receptacle limits
another opinion. 220.2(A) says 120 volts "unless another voltage is specified". The question specifies 115 volts, therefore the 20 ampere circuit capacity in volt-amperes is 115 X 20 =2300 volt-amperes. 220.3(B)(9) requires that receptacles be calculated at 180 volt-amperes. 2300 divided by 180 = 12.77, so the answer is 12.
Creighton.
another opinion. 220.2(A) says 120 volts "unless another voltage is specified". The question specifies 115 volts, therefore the 20 ampere circuit capacity in volt-amperes is 115 X 20 =2300 volt-amperes. 220.3(B)(9) requires that receptacles be calculated at 180 volt-amperes. 2300 divided by 180 = 12.77, so the answer is 12.
Creighton.