Re: commercial receptacle limits
To all Code Scholars and friends:
And now here's the rest of the story!
20 A x 115V (the
specified voltage)= 2300 VA
2300VA/180VA = 12.777 rounded down to 12 device yokes, or straps containing receptacles.
Section 220.3(B)(9) provides the 180 VA single, or multiple receptacle on one yoke.
This section also indicates that for a single piece of equipment, containing 4 or more receptacles, the computation is 90VA per receptacle.
Therefore, any yoke or strap that has 3 or less receptacles, is considered to be 180 VA.
Based upon the definition of "receptacle" in Article 100, the true answer to this question is:
12 yokes x maximum 3 receptacles per yoke = 36 receptacles.
The original question asked: "How many receptacles can be installed..."
Terminology is very important in writing defensible test questions, and with the answers
that were provided the question should have read,
"How many duplex receptacles can be installed on a 20 ampere, 115 volt branch circuit in a
commercial office building?"
Think real hard before putting your foot {now feet} into your mouth before you ask for the next dance!!
Joe Tedesco
www.joetedesco.com