By the NEC, it's not unless you decide to use it as such. Do you agree with that statement?
I think it is the exact same well casing with the exact same electrical characteristics relative to earth.... NEC or no NEC. Because of the relative sizes, the well casing has at least 25 times more contact with the earth than a ground rod.
As a grounding electrode it has a # 6 cu GEC ...or as in the OP a #4
As a metallic part likely to become energized it has a #12 cu or maybe #10 EGC.
What is the safety advantage to personnel being shocked by a fault to the casing in the pump circuit with a #12 EGC over a #6 GEC?
Think of the impedance created by the #12 that is only accessible to the lightning by way of the feeder EGC, to the branch circuit EGC, out an average 150' of overall wire length to get to the casing.
1. You think lightning is going to prefer that path over the rod?
2. Can you imagine the collateral damage throughout the home to all the other paths that are equally attractive?
I don't understand your point. "preferences" of lightning???
I started off my earlier post admitting that I don't know what to do with a well casing. I'm trying to understand and apply logic , common sense, and maybe a few electrical principles to the situation. The lightning doesn't know whether I decided to use the casing as a Grounding electrode or not. Would it burn off the smaller EGC with it's higher impedance more readily than if it were a # 6? I don't know.
How does the lightning get to the rod? Because of the considerably greater earth contact, would the lightning "prefer" the well casing over the ground rod? I don't know that either.
Most people do not put the well that far from the house ...the closer the cheaper. The well has to be 100 ft from the sewage disposal and the neighbors' sewage also has to be taken into account. Lots are expensive. the closer to the house the better.
Except for the difference in impedance of the # 10 or 12 and the #6, you're hooking them up the same way one way or another...
It's the same well casing. It's not a metal box hanging in a wooden stud wall. NEC or not, It's a grounding electrode with a #6 one way, and a grounding electrode with a #12 the other. I think the well casing should have the #6 cu . The OP is talking about someone running a #4.