No dispute with that. You can if that's what you want.I get .16 from a 20 va.
But you said you wanted 0.05mA.
Which is 0.06VA.
No dispute with that. You can if that's what you want.I get .16 from a 20 va.
Here in the US we use "trouble light" in two different senses:
1. A temporary with a cage shield and/or reflector light on a long cord used as a portable worklight, or
2. An indicator light showing that there is a problem.
.06VA would not do much for 1, but might be fine for 2.
Also, .5A instead of .5mA gives a much more believable result for 1.
Sent from my XT1585 using Tapatalk
The panel mounting 22mm indicator lamps we used are rated at 20mA. That's 400 times what the op says he wants.
Seems to me that something doesn't add up.
Is that 0.06A not 0.05mA as you stated earlier in the thread?The load of a the trouble circuit is actually .06 @120v a
If all you're doing is lighting up an indicator lamp, why not skip the transformer altogether and use a 24-volt lamp?
I was relaying what the contractor / customer stated to me.
Looking at the project Saturday the control circuit for signaling is fed from a 30va 120v to 24v.
The load of a the trouble circuit is actually .06 @120v and I found a piezo horn that is .058 also @ 120v which they did not tell me.
The control circuit powers a few proximity sensors and a control board. The label of the sensor system says up to 3w a 24v. So I believe the control power 30va @ 24v is sufficient.
24v 40va (trans) → reverse fed trans 20va 24v input -120v output → light/horn (.12a @120v)
So, what is the total 120v load?
Presuming that's 0.12a, you need (0.12 x 120) 14.4va, so a 24v @ 20va transformer would be ideal..12@120v
Sierrasparky;1942291[B said:].12[/B]@120v
So not 0.05mA as you previously stated.
Nor 0.005 mA?
Most of us here try to be helpful but if you continue to provide conflicting/duff information you must understand that makes it difficult.
Thank you all for your inputs.
Sorry , My OP was about was it ok to use a control trans in reverse , nothing more nothing less.
I gave the current requirements as was told to me.
I verified in person only yesterday.
What more do you want from me. Blood or something.
Speaking for most, if not all of us, we tend to try to be very specific and accurate, so we ask for the details we feel we need to give the correct answer to a generalized question.Thank you all for your inputs.
Sorry , My OP was about was it ok to use a control trans in reverse , nothing more nothing less.
I gave the current requirements as was told to me.
I verified in person only yesterday.
What more do you want from me. Blood or something.
Speaking for most, if not all of us, we tend to try to be very specific and accurate, so we ask for the details we feel we need to give the correct answer to a generalized question.
We're only trying to be helpful, not belittling. It's no always easy to give a yes-or-no answer to a yes-or-no question, especially for those of us who are (even quasi-) engineers.
180909-2432 EDT
Sierrasparky:
Any ordinary tightly coupled electromagnetic transformer can be driven from either the primary or secondary side. But you must stay below core saturation (volt-time integral), and within the power dissipation capabilities of the transformer.
You may not get quite the results you expect, but should be somewhat close. For example for a stepdown transformer the transformer turns ratio may be lower than the rated voltage ratio would indicate. This is to provide full output voltage at full load. When this transformer is run in reverse, then the output voltage will be less than what you might expect. But you won't exceed the volt-time integral if you provide somewhat greater input voltage.
.
.
I thought my OP was to the point. I am sorry if it confused some. I only knew what was told to me from the client over the phone. I asked for him to take a picture but he never did. I did the site visit and posted the corrected numbers. :?If you find it difficult to perfectly say what's in your mind, please try posting a schematic diagram instead,or a picture.
Just sound information.What more do you want from me. Blood or something.
Just sound information.
Other option is a relay with 24 volt coil to control the 120 volt indicator.
Then why mention itI was never asking anyone here about current