180916-2017 EDT
Back in post #52 I made a mistake in calculating the transformer internal impedance as viewed from the 24 V winding. The change in 24 V winding current with the 25 ohm load should have been 21.1/25 = 0.884 A instead of 0.17 A, and thus the calculated impedance on the 24 V winding side should be 5.5/0.884 = 6.52 ohms. Reflecting this to the 120 winding produces a result of 6.52*4.51^2 = 133 ohms.
So in my last test where the bulb current is 0.1 A on the 120 winding side I get a calculated change in voltage of about 133*0.1 = 13 V. The measured change was 108.4 - 93.5 = 14.9 V. Some of this 14.9 is a result of the drop in my test voltage source. Basically a good correlation.
.
Back in post #52 I made a mistake in calculating the transformer internal impedance as viewed from the 24 V winding. The change in 24 V winding current with the 25 ohm load should have been 21.1/25 = 0.884 A instead of 0.17 A, and thus the calculated impedance on the 24 V winding side should be 5.5/0.884 = 6.52 ohms. Reflecting this to the 120 winding produces a result of 6.52*4.51^2 = 133 ohms.