Can the disconnecting means for fixed electrical space heating equipment be mounted to the ductwork? If not, what section of the 2005 NEC prohibits that?
I agree with weressl. To add, I'm sure the manufacture instructions don't recommend this sort of an install.If not the word, the spirit of the NEC would be in disagreement.
The general concept being that electrical equipment is installed in and on places, surfaces and supports that are DEDICATED and DESIGNED for that purpose.
An air-conditioning duct is hardly something that is designed, sized and installed to provide structural support for anything. If the duct-work is modified, they need to call an electrician? If the NEC does not specifically prohibits this the HVAC codes may, so check that if you want to pursue this method of installation.
If not the word, the spirit of the NEC would be in disagreement.
The general concept being that electrical equipment is installed in and on places, surfaces and supports that are DEDICATED and DESIGNED for that purpose.
Check out 440.14
OK? Your point?
Do you claim anything to be there that is different from what I wrote?
OK? Your point?
Do you claim anything to be there that is different from what I wrote?
weressl said:If not the word, the spirit of the NEC would be in disagreement.
The general concept being that electrical equipment is installed in and on places, surfaces and supports that are DEDICATED and DESIGNED for that purpose.
Check out 440.14
It appeared to me you where indicating that mounting a disconnect in any space not dedicated and designed for that purpose would be against 'the spirit of the NEC'.
IMO 440.14 shows that there is no actual or 'spiritual'violation of the NEC.
I will also add that above ceilings it is very common practice to mount the disconnecting means for the various HVAC units right on the unit itself.
yes,,,,,you added "dedicated and designed",,,,,,,and 440.14 says no such thing
That's the equipment though, not the duct work.
Now that I have looked it up, I can't find anything that says you can't screw to the duct taking care not to damage the insulation of course.
IMO that would not be good workmanship.
I am surprised that we're even having this discussion.:roll:
The OP was asking could it be mounted on the duct workIt appeared to me you where indicating that mounting a disconnect in any space not dedicated and designed for that purpose would be against 'the spirit of the NEC'.
IMO 440.14 shows that there is no actual or 'spiritual'violation of the NEC.
I will also add that above ceilings it is very common practice to mount the disconnecting means for the various HVAC units right on the unit itself.
The OP was asking could it be mounted on the duct work