M. D.
Senior Member
Disposals are always fastened in place. Dishwashers are usually fastened in place. OP says they are using cord-and-plug which means a blender, toaster, or other can be supplied. The above section doesn't care that you wired a switch in place; Their total fastened load can only be half of the ratings.
I don't think you are correct,.. for what it is worth I think the wording stinks.
from 2010 ROP
_________________________________________________________
2-211 Log #4795 NEC-P02 Final Action: Reject
(210.23(A)(2) Exception)
_______________________________________________________________
Submitter: Adam J. Drozdowski, Artisan Electrical Contractors
Recommendation: Add the following new text:
Exception: When there is two or more receptacles used to supply a load for
utilization equipment fastened in place, it shall be permissible to use the full
allowable ampacity of the branch circuit if the receptacles are not readily
accessible.
Substantiation: The receptacles behind dishwashers, pigs, refrigerators, etc.
with cord and plug connection that are not readily accessible will not be
subjected to other loads of other equipment.
Panel Meeting Action: Reject
Panel Statement: The current rule only invokes the 50% limitation if the
branch circuit supplies, in addition to the fixed in place equipment, lighting
units, cord and plug connected equipment not fixed in place, or both. As such,
if the circuit supplies only equipment fastened in place, the full branch circuit
can be used.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12