Here is a solution for the customer that wants both.

Strangeservice002.jpg
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Sorry, hit post instead of preview. My guess is that this was originally a drop that was value engineered to underground. Overhead to underground is a common request here after hurricanes, but I have never seen this before.
 

jwjrw

Senior Member
Sorry, hit post instead of preview. My guess is that this was originally a drop that was value engineered to underground. Overhead to underground is a common request here after hurricanes, but I have never seen this before.

Other than height requirements is there any nec issues involved?
 

iwire

Moderator
Staff member
Location
Massachusetts
I have seen pictures of entire blocks like this when the utility deiced to move the overhead distribution underground.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Other than height requirements is there any nec issues involved?

IMO the NEC does not apply after the drip loop from the weatherhead.

You are correct, that would be POCO owned wire and conduit coming out of the ground. I posted this under 'Electrical Calculations/Engineering' because I just think it is a very unusual design for this area, I also see no NEC issues with this install.
 