- Lockport, IL
- Retired Electrical Engineer
The attached photo shows a handhole containing medium voltage cables and load break junctions. This is downstream of a fused disconnect within the service switchboard. I don't see an EGC being routed along with the MV cables entering the handhole. I don't think 250.190(C)(2) would allow the cable's shield to serve as an EGC. But looking at the photo, that is what I think I am seeing. I think the copper wire is a ground ring within the handhole, and the green flat thing is the cable's shield. Can anyone tell me whether I need to tell the owner that a wire-type EGC needs to be installed from the service switchgear to the ground ring within this handhole?