The attached photo shows a handhole containing medium voltage cables and load break junctions.  This is downstream of a fused disconnect within the service switchboard.  I don't see an EGC being routed along with the MV cables entering the handhole.  I don't think 250.190(C)(2) would allow the cable's shield to serve as an EGC.  But looking at the photo, that is what I think I am seeing.  I think the copper wire is a ground ring within the handhole, and the green flat thing is the cable's shield.  Can anyone tell me whether I need to tell the owner that a wire-type EGC needs to be installed from the service switchgear to the ground ring within this handhole?  
	
		
			
		
		
	
				
			 
				
 
 
		 
			 
 
		 
 
		