- Location
- Illinois
- Occupation
- retired electrician
I think he was after what I said in post 15.I'll buy that, I just had assumed that was where Dan was heading with this quiz. :smile:
I think he was after what I said in post 15.I'll buy that, I just had assumed that was where Dan was heading with this quiz. :smile:
Post 15The circuit conductor is not the conductor in each raceway...it all of the individual conductors that are connected in parallel. The code requires a 800 kcmil in each raceway, no matter how big or small the individual conductors that make up the circuit conductor are.
don_resqcapt19 said:I think he was after what I said in post 15.
necplus.org Staff Note for 250.122(F)
Where conductors are run in parallel raceways or cables as permitted by 310.4, each parallel equipment grounding conductor shall be sized per Table 250.122 based on the size of the overcurrent device protecting the conductors. In other words, the equipment grounding conductor in each raceway or cable must be full-sized, even though the ungrounded (phase) conductors are reduced in size.
I don't see anything on this link to help clarify??:-?
My mind is open to this discussion.
I would like someone to explain to me why (electrically speaking) the equipment ground conductor is required to be larger than the ungrounded conductor.
250.122(F) Conductors in Parallel.
Where conductors are run in parallel in multiple raceways or cables as permitted in 310.4, the equipment grounding conductors, where used, shall be run in parallel in each raceway or cable.
Each parallel equipment grounding conductor shall be sized on the basis of the ampere rating of the overcurrent device protecting the circuit conductors in the raceway or cable in accordance with Table 250.122.
necplus.org(not a formal interpretation) said:Staff Note for 250.122(F)
Where conductors are run in parallel raceways or cables as permitted by 310.4, each parallel equipment grounding conductor shall be sized per Table 250.122 based on the size of the overcurrent device protecting the conductors. In other words, the equipment grounding conductor in each raceway or cable must be full-sized, even though the ungrounded (phase) conductors are reduced in size.
I can see this being read either way. There is no solid code support for either interpretation of the interaction between 250.122(A) and .122(F). Without a code clarification, it is my reading that the sum of all of the conductors in parallel is the circuit conductor for the purposes of the application of 250.122(A).
My mind is open to this discussion.
I would like someone to explain to me why (electrically speaking) the equipment ground conductor is required to be larger than the ungrounded conductor.
As I see it, the size of the ungrounded conductor will restrict/determine how much current will flow in the fault current path, during a ground fault. Increasing the size of the EGC serves what purpose?
Pierre,I was under the understanding, that the overcurrent device was how we determined the size of the EGC, not the size of the conductors.
I am not too sure if I actually understand what you may be trying to tell us/me.
Makes sense to me.I am saying that ... the sum of all of the conductors in parallel is the circuit conductor, not the individual conductor in a single raceway.
Pierre,
I am saying that for the purposes of the rule in 250.122(A) that says the EGC is not required to be larger than the circuit conductors, that the sum of all of the conductors in parallel is the circuit conductor, not the individual conductor in a single raceway. The EGC is sized by T250.122 and the rating of the OCPD. In this example the rule in 250.122(F) would require a 800 kcmil EGC in each raceway, no matter what size the phase conductors in that raceway are.
Larry, just use the conduit.
Bob,Don
I respect your vast knowledge of the NEC. Its certainly much greater that mine. Your quote of 250.122(A) says
250.122(A) that says the EGC is not required to be larger than the circuit conductors. Circuit conductors Plural and not Circuit conductor singular. The circuit conductors in this case are 500 kcm.
It makes sense that the EGC would not be required to be larger that 500 kcm as Mr Piierre as said.