Haha, ok, I say it has to be full sized.
Ding-Ding-Ding!!!! We have another winner.....!:grin:
Haha, ok, I say it has to be full sized.
Soares Book on Grounding explains it this way:
In the event of a line-to-ground fault in the equipment suppolied by the circuit, the fault current should divide equally between the equipment grounding conductors. However, if a line-to ground fault occurs in the raceway or cable, current will be fed to the fault from both directions. The equipment grounding conductor will thus be called upon to carry the entire amount of fault current until the overcurrent protective device ahead of the fault opens.
In all cases the EGC must be 800 kcmil copper.
Interestly, in the 2002 code 310-4 included the clarification "(electrically joined at both ends to form a single conductor)". In 2005 the clarification omits 'to form a single conductor'. So are they saying since 2005 that parallel conductors are not considered a single conductor anymore?
Lori Fay
The 1971 NEC also has (electrically joined at both ends to form a single conductor) I think that it was added in the 71 NEC. The 1971 section is 310-10. You have raised an interesting question as far as the omission of this wording.(To form a single conductor).Interestly, in the 2002 code 310-4 included the clarification "(electrically joined at both ends to form a single conductor)". In 2005 the clarification omits 'to form a single conductor'. So are they saying since 2005 that parallel conductors are not considered a single conductor anymore?
Lori Fay
500 kcmil = #36000 OCPD feeding a 3 phase load
Raceway is PVC
1)Using 16 parallel sets of 500 kcmil
What size EGC is required in each raceway?
2)Using 15 parallel sets of 600 kcmil
What size EGC is required in each raceway?
3)Using 40 parallel sets of 1/0
What size is required in each raceway?
500 kcmil = #3
600 kcmil = #2
1/0 = #6
Partial post #64: ??And if that fault were to occur in the conduit with a single set of 500's its only going to carry the current of that single ungrounded conductor??
Not quite correct; the fault would carry current from both ends of the conductor through to the EGC; thus an oversized EGC is required by the NEC for parallel installations. Theoretically, one could expand upon the rule to see where certain boundary limits may need further clarification as in the example of many parallel runs, but the fundamental rule is sound.