Section 250.122(A) is titled "General". That tells me that the following subsections modify the general rule, just like in other areas of the code. So subsection (F) would prevail.
Larry, I agree 100%!
Section 250.122(A) is titled "General". That tells me that the following subsections modify the general rule, just like in other areas of the code. So subsection (F) would prevail.
I can see this being read either way. There is no solid code support for either interpretation of the interaction between 250.122(A) and .122(F). Without a code clarification, it is my reading that the sum of all of the conductors in parallel is the circuit conductor for the purposes of the application of 250.122(A).
250.122 Size of Equipment Grounding Conductors.
(A) General. Copper, aluminum, or copper-clad aluminum
equipment grounding conductors of the wire type shall not
be smaller than shown in Table 250.122, but in no case
shall they be required to be larger than the circuit conductors
supplying the equipment. Where a cable tray, a raceway,
or a cable armor or sheath is used as the equipment
grounding conductor, as provided in 250.118 and
250.134(A), it shall comply with 250.4(A)(5) or (B)(4).
(F) Conductors in Parallel. Where conductors are run in
parallel in multiple raceways or cables as permitted in
310.4, the equipment grounding conductors, where used,
shall be run in parallel in each raceway or cable.
Each parallel equipment grounding conductor shall be
sized on the basis of the ampere rating of the overcurrent
device protecting the circuit conductors in the raceway or
cable in accordance with Table 250.122.
Dan,
It is not clear because there is nothing that actually says the parallel conductors make up a single conductor. Without something that says that you can read it either way. You can also argue that if you use a 800 kcmil in each raceway, it is larger than the circuit conductors using the same logic that is used to require the 800 kcmil in each raceway. In the case of the 16 sets of 600s you have 6300 kcmil of circuit conductor and 12,000 kcmil of EGC.
250.122 Size of Equipment Grounding Conductors.
(F) Conductors in Parallel.
Where conductors are run in
parallel in multiple raceways or cables as permitted in
310.4, the equipment grounding conductors, where used,
shall be run in parallel in each raceway or cable.
Each parallel equipment grounding conductor shall be
sized on the basis of the ampere rating of the overcurrent
device protecting the circuit conductors in the raceway or
cable in accordance with Table 250.122.
310.4 Conductors in Parallel.
(A) General. Aluminum, copper-clad aluminum, or copper
conductors of size 1/0 AWG and larger, comprising each
phase, polarity, neutral, or grounded circuit conductor shall
be permitted to be connected in parallel (electrically joined
at both ends).
(E) Equipment Grounding Conductors. Where parallel
equipment grounding conductors are used, they shall be
sized in accordance with 250.122. Sectioned equipment
grounding conductors smaller than 1/0 AWG shall be permitted
in multiconductor cables in accordance with 310.13,
provided the combined circular mil area in each cable complies
with 250.122.
Wow, give us a chance to post!And the Winner is don_resqcapt19!!!!
Wow, give us a chance to post!
Ok, my answer=What Don Said! :wink::grin:Go ahead!:grin: There can be co-Winners!!:grin:
And, if that's the case, what would be the point of the specific paralleled-conductor EGC requirement?If that is the case we would only have to install an EGC in each raceway that matches the size of the phase conductors in that raceway.
Ok, my answer=What Don Said! :wink::grin:
Larry,And, if that's the case, what would be the point of the specific paralleled-conductor EGC requirement?
Larry,
You don't get to a case where the EGC in each raceway of a parallel set would have to be larger than the circuit conductors one of parallel raceways until you have at least 5 runs in parallel, so there is plenty of applications for the rule even if you never have to make the EGC larger than the phase conductors in that raceway.
You're kind of jumping pages there...that was not because of the use of parallel conductors, it was really because of the combination of the facts that your paralleled conductors are also tap conductors.I'm pretty sure I did it with two runs in parallel. See post #36
Soares Book on Grounding explains it this way:
In the event of a line-to-ground fault in the equipment suppolied by the circuit, the fault current should divide equally between the equipment grounding conductors. However, if a line-to ground fault occurs in the raceway or cable, current will be fed to the fault from both directions. The equipment grounding conductor will thus be called upon to carry the entire amount of fault current until the overcurrent protective device ahead of the fault opens.
lauraj, if you want a prize you have to answer the quiz:wink::grin: