"Each parallel EGC shall be sized on the basis of the ampere rating of the OCPD..."
I see no ambiguity. (310.4 is pretty clear too)

122(A) is titled "general"
122(F) is a specific application that IMO would over-ride 122(A)

That being said, I think I would be in favor of a change in the code to limit the size of the EGC in these extreme scenarios...but I won't let that impact what I think the code says today.:cool:
 
Anyone with a 2005 Handbook can go to Exibit 250.47 for the authors' reason for the

requirement, plus an illustration. It's located right after 250.122(F)(1) FWIW.
 