This part is compliant however he also needs to install ground rods unless he is connected to a concrete encased electrode- which I doubt.
Dennis.
What about 250.32(A) Exception ??
This part is compliant however he also needs to install ground rods unless he is connected to a concrete encased electrode- which I doubt.
Dennis.
What about 250.32(A) Exception ??
that would not be compliant. you cannot have your own set of grounding electrodes for these cables. you are required to use the ones that are supposed to already be there. there should be an intersystem bonding bridge for you to connect to.
Drive/bond two rods spaced 6ft. or better apart. Easiest Code compliance for second building grounding electrode system (GES) when no other electrodes are present... and a GES is required when supplied by feeder..... Should i suggest to the electrician to install a ground rod or just ask him his opinion on the matter?...
Drive/bond two rods spaced 6ft. or better apart. Easiest Code compliance for second building grounding electrode system (GES) when no other electrodes are present... and a GES is required when supplied by feeder.
Don't be like the inspectorThere is a 4x4 PVC box on the outside and the inside and joined with a piece of 1/2" conduit with a threaded adapter glued on each end and a nut inside the box, roughly in the middle of the back of both boxes. The question there is why not use a LB (conduit body) on the outside but i guess it works.
Even before NEC required us to install intersystem bonding devices - it still required those other systems to be bonded to the electrical system grounding system. You could drive all the rods you want to for a telephone or TV system, but the only way to ensure there is no potential between those systems and the electrical system is to bond them together at some point - that is just plain physics no matter what codes may be.Interesting, been doing that for years, not once has the inspector mentioned any problem with it. The local phone company also puts a ground rod at the phone line entry which is normally not on the same side of the house as the service entry and therefore no ground rod is nearby. Does the same rule apply to telco installs? I have seen the cable company do it as well, though most of the time they save the labor and money by putting the coaxial entry near the service entry and use that ground rod.
Anyway, spoke with the inspector, he approved the conduit install for the electrical install after reviewing the conduit and looking it up, it was listed and specified to be useable for direct burial and he claims he missed that the first time, and gave me the go ahead to back fill it and cleanup. He is requiring that the LB at the garage be removed and reinstalled without gluing it directly to the flexible conduit and put a threaded LB in its place and a connector on the conduit. Minor change, although it will require removing the sub panel and cutting off the conduit through the brick wall to replace it, but the electrician i just spoke with said he can get it all done in a hour.
.
The 12/3 feeds a panel with circuit breakers in a separate structure. I see it as a feeder.
Where are you getting that from?only if you're changing the overcurrent rating of the circuit. for example, you run a 10-3 to a 30am box with 2 x 20a breakers.
Feeder. All circuit conductors between the service equip-
ment, the source of a separately derived system, or other
power supply source and the final branch-circuit overcurrent
device.
If there is any overcurrent device (excluding supplemental overcurrent protection as an integral part of utilization equipment) installed in the circuit integral with or after the building/structure disconnecting means, the supply is a feeder. Refer to the Article 100 definition of a feeder.only if you're changing the overcurrent rating of the circuit. for example, you run a 10-3 to a 30am box with 2 x 20a breakers.
Where are you getting that from?
If you land in a box with breakers in it it's a feeder.
You can call them what you wish. That does not change the definition. Branch circuit comes after the final overcurrent.....Not necessarily. I've gotten into arguments with Madison inspectors on this. Often times I'll run a 12-3 MWBC from 20a 2-pole in the house to a 2 space panel with a 2-pole 20a breaker in the garage to serve as a disconnect. I called the wires between the house and the garage a branch circuit and I was correct. I could've also used molded case switches but they weren't available to me at the time![]()
Branch Circuit. The circuit conductors between the final
overcurrent device protecting the circuit and the outlet(s).
You can call them what you wish. That does not change the definition. Branch circuit comes after the final overcurrent.....
It's just the way it is.
Unless, of course you can justify categorizing the last as a "supplemental" OCPD rather than a branch circuit OCPD. This comes up from time to time when fused disconnects are used for a single HVAC on a dedicated circuit.You can call them what you wish. That does not change the definition. Branch circuit comes after the final overcurrent.....
It's just the way it is.
Unless, of course you can justify categorizing the last as a "supplemental" OCPD rather than a branch circuit OCPD. This comes up from time to time when fused disconnects are used for a single HVAC on a dedicated circuit.
Of course interpretations vary!
If you rationalize the definition and requirements surrounding supplementary overcurrent protection devices, you'll realize they cannot be installed anywhere in the branch circuit wiring, lest they become a branch circuit overcurrent device... which pretty much deduces to supplementary overcurrent devices must be internal to or integral with utilization equipment.Unless, of course you can justify categorizing the last as a "supplemental" OCPD rather than a branch circuit OCPD. This comes up from time to time when fused disconnects are used for a single HVAC on a dedicated circuit.
Of course interpretations vary!
If you rationalize the definition and requirements surrounding supplementary overcurrent protection devices, you'll realize they cannot be installed anywhere in the branch circuit wiring, lest they become a branch circuit overcurrent device... which pretty much deduces to supplementary overcurrent devices must be internal to or integral with utilization equipment.
Your typical fused disconnects for HVAC units cannot be supplementary overcurrent devices because you always have branch circuit wiring after them.
I'm not doubting they have no problem with you doing that... but are they telling you your supply is a MWBC or a feeder, or not telling you anything at all and just approving it?.... I was simply saying that the local inspectors in Madison, WI have no problem with me running a MWBC to a detached garage using a 2-space panel and 2-pole 20-amp breaker as a disconnect in lieu of a molded case switch and enclosure. The ampacity of the circuit remains the same and is disconnected common trip and the neutral and ground remain isolated.
I'm not doubting they have no problem with you doing that... but are they telling you your supply is a MWBC or a feeder, or not telling you anything at all and just approving it?
I have no problem with it myself... but no matter the rationale, it is non-compliant. :angel:Neither party is attaching any terminology to the installation. It's true that by definition, the wires between the breakers is a feeder, but both the inspector and I understand the intent of the NEC and both agree that adding a breaker in the garage poses no hazard and in fact encourages safety since there is a readily accessibly disconnect means nearby so a homeowner or future electrician doesn't attempt live work because they're too lazy to walk all the way down to the basement to disconnect the garage. Also the disconnect is in site.