Hi all,
I would appreciate some input on a problem I have. Say I have 4 THHN current-carrying conductors feeding 100A of noncontinuous load and 80A continuous. What size wire do I need for the feeder at 75` terminals. Here's what I did:
80 amps x1 = 80
100 amps x1=+100
180 amps
Since I have to derate by .8 for the 4 current-carrying conductors, I do not need to derate for the continuous load per 210.19(A)(1). 3/0 at the 90` column gives me 225 amps. 225x.8(4 current-carrying conductors)=180...enough to carry the load. So I got 3/0 copper. Can anyone confirm this. The thing I find odd is that if there were only 3 current carrying conductors, the wires would need to carry 200 amps as the calculated load.
80x1.25+100= 200 When I have 4 current-carrying conductors, it only needs to carry 180 amps as the calculated load. Thank you for any and all input
I would appreciate some input on a problem I have. Say I have 4 THHN current-carrying conductors feeding 100A of noncontinuous load and 80A continuous. What size wire do I need for the feeder at 75` terminals. Here's what I did:
80 amps x1 = 80
100 amps x1=+100
180 amps
Since I have to derate by .8 for the 4 current-carrying conductors, I do not need to derate for the continuous load per 210.19(A)(1). 3/0 at the 90` column gives me 225 amps. 225x.8(4 current-carrying conductors)=180...enough to carry the load. So I got 3/0 copper. Can anyone confirm this. The thing I find odd is that if there were only 3 current carrying conductors, the wires would need to carry 200 amps as the calculated load.
80x1.25+100= 200 When I have 4 current-carrying conductors, it only needs to carry 180 amps as the calculated load. Thank you for any and all input