bob said:
The statement "but after any such adjustment, such feeders are only required to have an ampacity of 100% non-continuous plus _100%_ of continuous." is meaningless.
You determine the Minimum Ampacity based on the 100% non-continuous plus _125%_ of continuous load. Pick a conductor. Then you make the adjustments to the ampacity of the conductor based on the 90C ampacity if it is rated at 90C. After the adjustments the conductor still must meet the Minimum Ampacity at 75C. You do not apply the 125% again. It is already in the minimum requirements.
This is _exactly_ the issue being discussed. You have just asserted one of the possible readings of the code, but without supporting this interpretation.
NEC 215.2(A)(1):
[BGeneral.[/B] Feeder conductors shall have an ampacity no less than required to supply the load as computed in Parts II, III, and IV of Article 220. The minimum feeder-circuit conductor size, before the application an any adjustment or correction factors, shal have an allowable ampacity not less than the noncintinuous load plus 125 percent of the continuous load.
As I read this:
Conductors are required to have an ampacity not less than the load served. I read this to mean 100% non-continuous plus 100% continuous.
Next, the conductor is required to have an ampacity
before the application of any adjustment or correction factors of 100% non-continuous plus 125% continuous. This makes it clear that in the most common use of the conductors, the requirement is 100% non-continuous plus 125% continuous.
As I read this, the 100% requirement _always_ applies, but the 100% plus 125% requirement only applies to the most common situation, when no adjustment factors apply.
In the present example, the OP gave us 100A non-continuous + 80A continuous loading, but also an adjustment factor of 0.8. This 0.8 adjustment factor applies to the 90C ampacity.
As I read 215.2(A)(1) this tells us that the minimum conductor ampacity is 180A, and that
additionally the minimum conductor ampacity
before any adjustment is 200A. The minimum conductor ampacity is determined at 75C, the terminal rating of the attached devices. After any adjustment factors are applied, an ampacity of 180A is sufficient to meet the requirements of 215.2(A)(1). This adjusted ampacity may be determined from the 90C conductor rating.
(Note: As I've stated above 215.3 and 240.4 and 240.6 also play into conductor sizing.)
-Jon