greeny
Member
- Location
- Southern NH
Charlie, thank you so much for your input. I can see the light This all makes sense to me now that you have explained it in a methodical manner. At no point can the conductor's ampacity at it's "operating" temperature ever exceed 125% of the continuous load plus the noncontinuous. But when we have correction factors and adjustments, we start with the conductor's temperature rating and we never need to apply the 125% factor to the load, continuous or not. The conductor ampacity must be able to satisfy both conditions. And yes, Charlie, I believe that was the thought process of the instructor I had. It just went a wee bit over my head