Sizing Conductors, Jon and I against the world!
Sizing Conductors, Jon and I against the world!
Charlie, Bob, Winnie
A few months behind but I'm with Winnie. I think the key to the proof of accurate interpetation is the difference in "Minimum Ampacity" and "Minimum Size" as Charlie pointed out.
110.14(C) Temperature Limitations, requires me to use the temperture rating associated with the ampacity of a conductor based on the temperature rating of the connection(s). Also, I am permitted to use higher temperature rated conductors only for adjustment, correction, or both.
Paraphrasing even further, To me this means that anytime I want the ampacity of a conductor I use the 60 or 75 degree temperature column of Table 310.16 but if I have 90 degree wire then I can use that column only for the purposes of adjustment(>3 conductors) or correction (Ambient Temp.)
Back to 210.18(A), if we go down the Branch-Circuit road, The first sentence dictates the minimum ampacity can not be less than the max load. (100% continuous or not) To find the ampacity I should use the 75 degree column for the previous examples. If I need to adjust or correct and I have 90 degree wire I can use the 90 degree column. Based on my read of 110.14(C) I have two minimum ampacities, always, one at 75 degrees protecting the circuit breaker from overheating because of the connection and sometimes, two protecting the condutor from overheating because of more than 3 CCC's or higher Ambient Temp. For the the second min ampacity I can use the 90 degrees column if that matches the wire.
Now moving on to the "Minimum ... Conductor Size" mentioned in the second sentence of 210.19(A)(1) Now an additional minimal requirement is that the ampacity must not be less than 125% cont. + 100% non cont. before adj. or corr. factors. I believe the code uses the terminology "min ... cond size" in a
failed attempt to be clear/accurate/consistent. "Before the application of any adjustment or correction factors" is almost the same thing as saying don't use the 90 deg column and don't adjust the numbers in the table for raceway fill or ambient temperature. (Remember you can only use the 90 deg column for adjusting and correcting.) This second minimal requirement is also designed to protect the circuit breaker. (or other component) By requiring the conductor to be larger the temperature of the conductor at the breaker lug under the same load will be less. Circuit breakers are normally tested at 80% of their rated load for continuous operation. Sometimes they are tested and listed to operate continuous at 100% rated load. In this case the Exception lets you out of the 125% requirment.
In this case it seems to me that if you read the sections mentioned here and take them at face value word for word, especially emphasising the two seperate requirements of minimum ampacity and minimum size then you will agree with Winnie.
I hope that the next code cycle will clarify this. The problem is to write the code to be accurate and to avoid requiring overdesign and at the same time avoid requiring to many steps just to size a conductor and to make it plain. It did't take long searching the internet and this site to see that a lot of pretty smart and code educated people see it different ways.
Ed Jackson, PE
Why can't we all just get along?