I am working on this job with RED Fpe Stablok breakers. When closing a metal j box "power on" an old nicked wire made contact with the side of the box but did not trip the breaker, it literally blew the wire in half! So for knowledge I went back to the panel and directly connected a piece of wire to a different RED Fpe breaker in the panel and shorted the other end on purpose to ground to see the result. That breaker did not trip either. It blew the end off the wire!
I really need input on this when if I encounter more of the panel.
Is the black handle Stablock different? or the same problem. I was told black handle pink label are ok. Is this true?
The grey cased Canadian Replacement is that better?
I really need input on this when if I encounter more of the panel.
Is the black handle Stablock different? or the same problem. I was told black handle pink label are ok. Is this true?
The grey cased Canadian Replacement is that better?