I could put a blank cover on this and it is still an outlet.
An outlet is not always the last point on any wiring system.
This, to me, is a junction box with conductors dead ending in it. The ability in the future to configure it differently does not govern what it is now.
There is no supply-to-load complete circuit, and/or, there is no defined outlet such as a receptacle device, nor is there a connection of the Branch Circuit Conductors to the conductors of Utilization Equipment.
This is, as shown, merely a means to hold the end of a cable in an approved manner.