I'm thankful that I didn't get injured from the arc flash. :thumbsup:
my 15 kCal blast suit is only for 480v & more.
Good info to know. This happened 18 years ago so the chances of me going back to say "Sorry about your breaker panel, I'd like to replace it because I scraped off the plating and used self-tapping screws for the ground bar" is a shot in a million.Panel bus probably should have been replaced also in that situation. Homeline bus is tin plated aluminum, filing off anything leaves you with just aluminum wherever you do this.
self tapping screws - in particular a coarse threaded screw - leaves you with less thread contact in the metal then a machine thread screw - plus the factory bonding screw location is machined to make thicker wall at the point the screw is installed to make more thread contact depth. Add to that if the bonding screw wasn't tight enough you have additional arcing at that weak connection point(s)
That's nice to know. If I knew it might have happened I might have worn one if I had one.my 15 kCal blast suit is only for 480v & more.
This is a great thread. What if, instead of a $10 Kenny clamp, one were to install a simple $.25 1/2" pvc connector only. Would that be a violation? What if a small section of pvc were connected to the connector to create a sleeve for the GEC to enter the panel?
May be a Code issue there with a "dry location" if those are listed as such. But, practically speaking, there's no difference I can think of, assuming installed on bottom, of course.
We are talking about a GEC. Do you think a GEC requires a dry location? They get sleeved in PVC all the time to keep from having to bond the GEC to the raceway.
Is that an opinion or a fact? Most inspectors around here are not going to care if they call it a GEC KO or a drainage KO. House A has Sq D Meter pan next door house B has Milbank, does the inspector care if each uses that KO for the GEC?
250.4(A)(1) Electrical systems that are grounded shall be connected to earth in a manner that will limited the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and that will stabilize the voltage to the earth during normal operation. ( Listed Fittings will limit sideflash NFPA 780 Lightning Protection)
• 250.8 Connection of Grounding and Bonding Equipment Grounding and bonding conductors are required to be installed with a listed fitting.
• 250.64(B) Securing and Protection from Physical Damage
Provides proper strain relief required by the UL/ANSI Standards
UL 467 Grounding and Bonding and UL 486A for Connectors, see
Annex A, NEC.
• 250.64(E) Enclosures for Grounding Electrode Conductors
Using a rigid coupling and a Kenny clamp®, one can bond both ends of a raceway without bending the conductor through a lug connected to a bond bushing.
• 300.15 Boxes, Conduit Bodies, or Fittings – Where Required Fittings and conductors shall be used for the specific wiring method for which they are designed.
• 312.5(A) Openings to Be Closed. Openings through which conductors enter cabinets, cutout boxes and meter enclosures shall be adequately closed.
Amen brother well said.For lack of a connector.....guess who's liable....
~RJ~
What you posted is Kenny's opinion of what code requires, not what code says.So, here are the code issues (from Kenny)>>>
entity points out the violations using the codes posted above
~RJ~
I have ask and no one has answered a simple question. If 250.64(E)(1) requires both ends of rigid meal conduit to be bonded to the conductor why is a meter pan not required to be bonded.
As s code official I could care less what someone writes in their paper work all I am interested in is 110.3(B) what does a third party say the hole is for and not one says for the GEC
If the conductor terminates in the meter pan where is "the other end" that needs bonded? You are not passing through you are entering and terminating within, plus it generally is terminating on something that already is bonded to the pan.Amen brother well said.
I agree, I also think most points made there are emphasizing things NEC maybe sheds a little light on but nothing in NEC actually requires a fitting such as the kenny clamp.What you posted is Kenny's opinion of what code requires, not what code says.
Mike Holt drawings often (maybe even always) show some sort of fitting where a GEC enters such enclosures. You any find any of his literature that says there must be such a fitting there?thank you Mike
250.64(E) addresses (main passage)>>> Ferrous metal raceways and enclosures <<<<
an 'enclosure' can be meter, panel, troff, JB, etc
Mike Holt himself portrays this in his literature>
~RJ~
I don't write this stuff or even make it up but I will copy and paste itIf the conductor terminates in the meter pan where is "the other end" that needs bonded? You are not passing through you are entering and terminating within, plus it generally is terminating on something that already is bonded to the pan.
So what do you do Mike, run a jumper to the top of the panel or meter can even though the GEC doesn't exit it? IOW's the GEC is terminated (as in connected and stops) so there is no "each end" only "one end"I don't write this stuff or even make it up but I will copy and paste it
Ferrous metal raceways and enclosures shall be bonded at each end of the raceway or enclosure to the grounding electrode or grounding electrode conductor.
...Given i've run many a GEC thru a 1/4" hole, one can imagine the choke effect (as stated in UL & EE level literature) 97% ...
Roger
Please cite this more specifically so I can see the exact wording as it applies to entering a 1/4" KO of a thin-walled enclosure.