If the generator used with the interlock kit is a listed portable generator, the failure would be based on 110.3(B).Based on what? I would be calling the DCA before the ink dried on the red sticker.![]()
If the generator used with the interlock kit is a listed portable generator, the failure would be based on 110.3(B).Based on what? I would be calling the DCA before the ink dried on the red sticker.![]()
If the generator used with the interlock kit is a listed portable generator, the failure would be based on 110.3(B).
The gernerator listing requires the use of transfer equipment that switches the grounded conductor.Which part of 110 would specifically apply? And wouldn't that apply later when the generator is actually connected? For now an inlet box and an interlock would be compliant no?
The gernerator listing requires the use of transfer equipment that switches the grounded conductor.
Because the installation has only one use...to connect a portable generator to the buildings electrical system.Let's say for the sake of this thread there is no generator. Just an inlet box and a listed interlock, how does that violated the NEC?
Because the installation has only one use...to connect a portable generator to the buildings electrical system.
Also is the interlock listed as "transfer equipment"? 702.5 requires the use of "transfer equipment".
That center rib of the panel cover holds the breakers "in place". I didn't mean to infer that it held a breaker securely in place. But, you can't remove the breaker with the cover on can you ?Since when did the panel cover hold in the breakers? IMO if a plug on breaker will not stay attached to the bus without the cover, you have a weak connection waiting to make for additional problems.
However, it is not used in the NEC.Anything is possible with IF
That center rib of the panel cover holds the breakers "in place". I didn't mean to infer that it held a breaker securely in place. But, you can't remove the breaker with the cover on can you ?
BTW, I just remembered another reason why some inspectors won't allow interlock kits. I've had some tell me that they've seen instances where the main breaker did not disconnect from the utility when operated. "What if that happens ? "
IMHO, once you use that tiny little 2 letter word IF, anything can be possible
Anything is possible with IF
- What IF the main breaker doesn't disconnect from the utility ?
- What IF the main breaker only disconnected one phase ?
- What IF a downed tree disconnects your triplex from the house and the POCO mis-connects when they power back up ?
- What IF a plane crashes in your back yard and you lose power ?
- What IF you won the $320 Mil lottery today and couldn't find your ticket ?
The code section clearly requires the use of "transfer equipment" and goes on to describe the function of transfer equipment. While I fully agree that the interlock kit provides the required functionality of "transfer equipment" they are not transfer equipment unless so listed.First sentence of 702.5: "Transfer equipment shall be suitable for the intended use and designed and installed so as to prevent the inadvertent interconnection of normal and alternate sources of supply in any operation of the transfer equipment."
Interlock kits meet this requirement, nothing in that article mentions listing requirements. I am open to suggestions of requirements if they have good backing, I just need more than what was presented so far on this one to convince me there is something wrong with it.
Where is it required that the neutral must be switched? If one were to install a genuine transfer switch I would guess 99% of the time it still wouldn't switch the neutral, but nobody would question it either.
Including what IF a transfer switch fails to disconnect one line from the utility side?
Or what IF you turned off a breaker for servicing something and at least one pole never opened?
The dead front of a panelboard is there to close up the front side of the panelboard. It may help some in keeping breakers in place. I have mostly seen this need in FPE panels and GE 1/2 size breakers. (You get what you pay for)
The cover provides no securing in a panel with bolt on breakers.
I agree with you both.:happyyes:Roger said:However, it is not used in the NEC.
This is the argument that jwelectric has posed and it's a valid argument. If we all accept this as being Gospel then there's no point in talking about interlock kits with listed generators under 15KW. By the same token you would not be able to use any of the Reliance transfer panels as they do not transfer the neutral. The only chance you might have is if they made a multi-switch transfer panel (similar in style to the Reliance units) with multiple EZ-generator switches like the ones shown here : http://www.ezgeneratorswitch.com/ . In this case you would have to hard-wire in each branch circuit as these switches transfer the neutral.The code section clearly requires the use of "transfer equipment" and goes on to describe the function of transfer equipment. While I fully agree that the interlock kit provides the required functionality of "transfer equipment" they are not transfer equipment unless so listed.
As far as the requirement to switch the neutral, it only applies to listed portable generators, 15kW or less used to supply power to a building. The requirement is found in the UL Guide Information for "Engine Generators for Portable Use" (FTCN). The requirement does not appear in the Guide Information for "Engine Generators" (FTSR). The generators covered by FTSR are intended for stationary and not portable use.
What IF a downed tree disconnects your triplex from the house and the POCO mis-connects when they power back up ?
I know, it seems ridiculous right ? I once got a call from a customer after a storm and a downed power line. When POCO reconnected her they spliced both of the ungrounded conductors to the same phase. It was at a point on the utility pole where several other customers were also connected. The call I got was that her electric range didn't work.:roll:What? :?
Note that this would only apply if you are using a generator of 15kW or smaller that is listed as a portable generator. In many states there is no requirement to use a listed generator and there are many portable generators that are not listed.This is the argument that jwelectric has posed and it's a valid argument. If we all accept this as being Gospel then there's no point in talking about interlock kits with listed generators under 15KW. By the same token you would not be able to use any of the Reliance transfer panels as they do not transfer the neutral. The only chance you might have is if they made a multi-switch transfer panel (similar in style to the Reliance units) with multiple EZ-generator switches like the ones shown here : http://www.ezgeneratorswitch.com/ . In this case you would have to hard-wire in each branch circuit as these switches transfer the neutral.
Doing illegal un-permitted work so you can use equipment you seem to know they would turn down.
I fail to see the license making a difference.
If they are not informed, it doesn't take too long to figure it out, or worst case they end up paying for a service call to get educated on the matter.From my observation, may of the portable generators used by home owners are undersized for their full home loads. How do these accessories that effectively make the service pannel into a piece of manual transfer equipment, ensure compliance with 704.2(B)(1)?Are we to assume the installers will provide adiquate instructions to the homeowners regarding the turning off of certian breakers to bring their load down to a level that their generator can serve? ... i.e., turn off the pool pump, sauna, AC, ... .
702.4 Capacity and Rating
(1) Manual Transfer Equipment.Where manual transferequipment is used, an optional standby system shall haveadequate capacity and rating for the supply of all equipmentintended to be operated at one time. The user of the optionalstandby system shall be permitted to select the load connectedto the system.