I should have elaborated that it only needs a shunt around the current sensing coil.mivey said:No. It does not need a ground for the test button to work.
I should have elaborated that it only needs a shunt around the current sensing coil.mivey said:No. It does not need a ground for the test button to work.
CLUCK CLUCK CLUCK CLUCK CLUCK!!!!!!!!gar said:080730-2303 EST
I just put some of the pieces back together and I have found that the extra power switch contacts contact the back output terminals for additional outlets. The other contacts mentioned in my previous post only supply the slots in this GFCI receptacle.
.
First sentence, incorrect. However, a plug-in tester does need the EGC.jinglis said:A GFCI does need a ground in order for the test button on the unit to work. It does not need a ground conductor in order to functon properly under a ground fault condition.
gar said:080739-2251 EST
Electronically it may work well. On the negative side there did not appear to be any flux removal from hand soldered high current areas,
.
It was a hilti te 12 I believe. Plastic 2w cord in a pouring rain condition. Gun was soaked wooden ladder was soaked I was soaked head to toe. No metalic case.gar said:080731-0648 EST
quogueelectric:
I believe in your example you had a drill motor with a metalic housing connected to the EGC (ground wire) in a three wire cord with a three prong plug.
When the ground terminal of the GFCI was floating the fault current from the drill contacting a hot wire flowed thru you to the wet floor. There was nowhere for it to go at the GFCI and it flowed thru you.
After you connected an EGC conductor from the main panel to the ground terminal on the GFCI, then you provided a path for the fault current to the drill to its case to the drill's EGC, to the drill plug ground pin, to the GFCI ground pin, and to the EGC back to the main panel. I would not expect you to get a shock in this instance because the housing of the drill probably only rises a few volts above the earth potential.
Whether the GFCI tripped and/or the main breaker tripped is not clear when you had the EGC ground terminal correctly connected (meaning connected).
What I have just said has been mentioned in previous posts.
With a non-GFCI receptacle and the ground pin correctly connected to an EGC to the main panel I would not expect you to get a shock. Thus, the GFCI probably had nothing to do with whether or not you got a shock.
.
crossman said:Thank you GAR for the work and your findings. Very interesting indeed.
gar said:Looks like Leviton has a unique competitive advantage unless others have licensed or been able to get around Leviton patents.