Code reference :thumbsup:
210.12(A)(1)
Code reference :thumbsup:
210.12(A)(1)
Nowhere does it say only A 1. They give you several options.
It does not specifically say AFCI circuit breaker. You are correct with that point. However, you posted a link of an AFCI receptacle. The AFCI receptacle would not provide AFCI protection for the entire circuit as it states in 210.12 (A)(1). My post earlier stated installing a new circuit from a Zinsco panel and that you can not get an AFCI circuit breaker for a Zinsco panel. In that circumstance the Zinsco panel should be replaced.
(4) A listed outlet branch-circuit type arc-fault circuit interrupter
installed at the first outlet on the branch circuit
in combination with a listed branch-circuit overcurrent
protective device where all of the following
conditions are met:
a. The branch-circuit wiring shall be continuous from
the branch-circuit overcurrent device to the outlet
branch-circuit arc-fault circuit interrupter.
b. The maximum length of the branch-circuit wiring
from the branch-circuit overcurrent device to the
first outlet shall not exceed 15.2 m (50 ft) for a
14 AWG conductor or 21.3 m (70 ft) for a 12 AWG
conductor. c. The first outlet box in the branch circuit shall be
marked to indicate that it is the first outlet of the
circuit.
d. The combination of the branch-circuit overcurrent
device and outlet branch-circuit AFCI shall be identified
as meeting the requirements for a system
combination–type AFCI and shall be listed as such.
It would if the run is under 50 feet on #14.
Which brings me to my point, you still need to install an AFCI circuit breaker on the new circuit unless you comply with 210.12(A)(5 & 6).
Explain:thumbsup:
Read the code.:thumbsup:
Read the code.:thumbsup:
I have, can you point to the exact set of words which forbids it?
Chris1971 isn't wrong.
Ponder this phrase from the section you quoted:
"......in combination with with a listed branch-circuit overcurrent protective device......."
Minimal business is lost (if any?) when a customer doesn't want they're old obsolete fuse or breaker panel replaced.
It was the intent of the breaker manufacturers, then the device manufacturers wanted in on this as well.I've brought this up before, only to get shot down. Is the intent really to have an AFCI breaker? If it is then why offer an AFCI receptacle?
Part (d) is the key part, "The combination . . . shall be identified as meeting the requirements for a system combination–type AFCI and shall be listed as such."Is the intent really to have an AFCI breaker? If it is then why offer an AFCI receptacle?
Part (d) is the key part, "The combination . . . shall be identified as meeting the requirements for a system combination–type AFCI and shall be listed as such."
What's the latest on this, has UL even developed a listing standard for complying with 210.12(A)(4)?
Cheers, Wayne
But why make it so obscure? I've brought this up with electricians who say they install the outlet and not worry about the breaker. There are DIY videos by Leviton and P&S which do not tell the HO to change the breaker.
It is a bit obscure because a standard breaker is a listed overcurrent protective device. However, why do we think after all the discussion about protecting the the wire at the source that they would allow an afci receptacle and not protect the wiring ahead of it.... One would have to assume the 2 units would have to work together. I admit I had trouble with the wording originally also.
I've brought this up before, only to get shot down. Is the intent really to have an AFCI breaker? If it is then why offer an AFCI receptacle?
It was the intent of the breaker manufacturers, then the device manufacturers wanted in on this as well.
I've brought this up with electricians who say they install the outlet and not worry about the breaker. There are DIY videos by Leviton and P&S which do not tell the HO to change the breaker.
I agree w/ this answer
V V V V V
Plus they had to come up w/something to push afci protection into older homes w/ panels that wouldn't accommodate their breakers.
And????
It is not required to change the breaker to afci when modifying an existing circuit/changing a device per 210.12(B)(2) and 406.4(D)(4),
changing the breaker is only an option, you can do an obc afci in lieu of swapping the breaker.....
Now if they are saying that you can do that w/ a new branch ckt w/out meeting 210.12(A)(2),(5) or (6), that's an issue if they are under the 2014.
I don't know why 210.12(A)(4) is around as it makes no sense to say you can do it w/out there being an approved product that meets the criteria in the first place.
So basically what they are saying is that you are supposed to use an AFCI breaker BUT because you can't always do that lets just be vague and let people decide based on desired interpretation? :blink: