When the concrete encased electrode 4 AWG copper is too short to reach the service entrance (meter socket) -can it be spliced without Exothermic or Cad Welding? I heard there is a split-bolt for this purpose -can any one elaborate on this?
 

pierre

Senior Member
Re: Ground Conductor Splicing

To elaborate on Ryan's post, the GEC is required to remain unbroken and unspliced it's entire length. You are permitted to splice it though if you use a exothermic splice (such as Cadweld) or an irreversible crimp type splice. You are not permitted to splice with split bolts.
 

rcaron

Member
Re: Ground Conductor Splicing

Pierre,

I heard there is a spli-bolt that once tighten/torqued that head snaps off and makes it not removable -ever heard of such a thing?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: Ground Conductor Splicing

If the concrete encased electrode is a supplemental grounding electrode the conductor can be spliced with a split bolt.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Ground Conductor Splicing

If the uffer conductor was routed to say the water line it could be spliced as it would be a bonding jumper not a GEC. :cool:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: Ground Conductor Splicing

Originally posted by ryan_618:
Originally posted by infinity:
If the concrete encased electrode is a supplemental grounding electrode the conductor can be spliced with a split bolt.
What code section are you basing this on?
250.53(D)(2)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: Ground Conductor Splicing

How does that except out 250.64(C)?
250.64(C) is for Grounding Electrode Conductors, the conductor from the supplemental electrode is not a GEC so 250.64(C) would not apply. If you look at 250.53(D)(2) you will see that the supplemental conductor is permitted to be directly connected to the GEC.

[ December 06, 2005, 06:18 PM: Message edited by: infinity ]
 

ryan_618

Senior Member
Re: Ground Conductor Splicing

Using a split bolt doesn't create a splice though.

You can connect any bonding jumper to the grounding electrode conductor if you use a split bolt, becasue a split bolt is not a splice.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Re: Ground Conductor Splicing

Sorry, infinity, but it looks the the supplemental's conductor can be bonded to, but not be, the GEC, as I read it.

If the conductor can reach one of the items mentioned, then it can be bonded to it. Extending it, hmmm... Maybe, maybe not.

[ December 10, 2005, 12:09 AM: Message edited by: LarryFine ]
 

eprice

Senior Member
Location
Utah
Re: Ground Conductor Splicing

I agree with what iwire said. A conductor that is not the GEC, but is a bonding jumper between grounding electrodes, can be spliced by reversible means. 250.53(C) requires the bonding jumpers to conform to 250.64(A), (B), and (E). It does not require them to conform to 250.64(C).
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: Ground Conductor Splicing

Originally posted by eprice:
I agree with what iwire said. A conductor that is not the GEC, but is a bonding jumper between grounding electrodes, can be spliced by reversible means. 250.53(C) requires the bonding jumpers to conform to 250.64(A), (B), and (E). It does not require them to conform to 250.64(C).
Thanks Eprice,

I was trying to say the same thing this morning until my PC froze and lost my post.


Trevor
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: Ground Conductor Splicing

Originally posted by rcaron:
When the concrete encased electrode 4 AWG copper is too short to reach the service entrance (meter socket)...
Is the #4 CU the grounding electrode, or the Grounding Electrode Conductor to the electrode? If the #4 in question is the electrode, then run a GEC sized according to 250.66 to an accessible location and splice the electrode to the GEC using any reversible method. The GEC must be continuous between the service and the electrode. :)

A water pipe is not continuous to the electrical service. That's why we have Grounding Electrode Conductors. ;)
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Ground Conductor Splicing

Originally posted by georgestolz:
]Is the #4 CU the grounding electrode, or the Grounding Electrode Conductor to the electrode?
The electrode 'stops' when it is encased with less than 2" of concrete.

Check out 250.52(A)(3).
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: Ground Conductor Splicing

Around here, the Ufer is allowed to protrude from the foundation for the connection of the GEC.

See 250.68(A):
Exception: An encased or buried connection to a concrete-encased, driven, or buried grounding electrode shall not be required to be accessible.
What that does not say is that the connection shall be required to be encased.

I could purchase a ten foot ground rod, drive it 8', and connect to the top of the ground rod.

The water metal pipe is for 10' underground. Prior to (...what, 96?) the existing wording coming into being, beyond 5' inside was considered part of the electrode to be used for interconnection of electrodes. Then the point of connection was limited to 5'. The electrode is still the same old electrode, it's underground. But it's understood that if the electrode is continuous to an accessible point, we're permitted to tie into that accessible point.

The business end of a Ufer must be 20' long, but there is no limitation on how long it can be. The business end must be encased by 2" of concrete, but obviously if you were to attempt to pull the electrode to the service as some do (and as the original poster appears to do), at some point you would have to leave the bottom of the foundation or footer, and shed the 2" of encasement.

Unless you bury the back of your service 3" into the foundation wall. :)

[ December 08, 2005, 08:43 AM: Message edited by: georgestolz ]
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Ground Conductor Splicing

George I am sorry we are butting heads so much lately. :(

Originally posted by georgestolz:
Around here, the Ufer is allowed to protrude from the foundation for the connection of the GEC.

See 250.68(A):
Exception: An encased or buried connection to a concrete-encased, driven, or buried grounding electrode shall not be required to be accessible.
What that does not say is that the connection shall be required to be encased.
The point of connection is irrelevant.

Consider a continuous piece of 4 AWG copper 200' long, 100' of it is encased in the concrete footing, 100' of it runs through the building to the service.

That continuous conductor stops being a concrete encased electrode when it has less than 2" of concrete encasement.

From that point on it is either a bonding jumper or a GEC.

Originally posted by georgestolz:
Comparing the Ufer to the water pipe,
That is comparing apples to oranges.

The code tells us a concrete encased electrode is encased in concrete.

The code does not say that the water pipe must be completely buried.

A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing effectively bonded to the pipe) and electrically continuous (or made electrically continuous by bonding around insulating joints or insulating pipe) to the points of connection of the grounding electrode conductor and the bonding conductors.
Or simplified.

A metal underground water pipe in direct contact with the earth for 10 ft or more and electrically continuous to the points of connection of the grounding electrode conductor.

Bob

[ December 08, 2005, 01:46 PM: Message edited by: iwire ]
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: Ground Conductor Splicing

Originally posted by iwire:
George I am sorry we are butting heads so much lately. :)

A concrete encased electrode is a highly similar concept to water pipe. A water pipe is a dirt-encased electrode. :)
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Ground Conductor Splicing

George the wording describing a water pipe grounding electrode and a concrete encased electrode are quite different.

A concrete encased electrode can not exist outside of concrete, not possible.

A water pipe grounding electrode can and does exist outside of the ground up to 5'.

Read the sections carefully using "Charlie's Rules".

Forget what you have done or what you think they should mean.
 