What code section are you basing this on?Originally posted by infinity:
If the concrete encased electrode is a supplemental grounding electrode the conductor can be spliced with a split bolt.
250.53(D)(2)Originally posted by ryan_618:
What code section are you basing this on?Originally posted by infinity:
If the concrete encased electrode is a supplemental grounding electrode the conductor can be spliced with a split bolt.
How does that except out 250.64(C)?Originally posted by infinity:
250.53(D)(2)Originally posted by ryan_618:
What code section are you basing this on?Originally posted by infinity:
If the concrete encased electrode is a supplemental grounding electrode the conductor can be spliced with a split bolt.
250.64(C) is for Grounding Electrode Conductors, the conductor from the supplemental electrode is not a GEC so 250.64(C) would not apply. If you look at 250.53(D)(2) you will see that the supplemental conductor is permitted to be directly connected to the GEC.How does that except out 250.64(C)?
Thanks Eprice,Originally posted by eprice:
I agree with what iwire said. A conductor that is not the GEC, but is a bonding jumper between grounding electrodes, can be spliced by reversible means. 250.53(C) requires the bonding jumpers to conform to 250.64(A), (B), and (E). It does not require them to conform to 250.64(C).
Is the #4 CU the grounding electrode, or the Grounding Electrode Conductor to the electrode? If the #4 in question is the electrode, then run a GEC sized according to 250.66 to an accessible location and splice the electrode to the GEC using any reversible method. The GEC must be continuous between the service and the electrode.Originally posted by rcaron:
When the concrete encased electrode 4 AWG copper is too short to reach the service entrance (meter socket)...
The electrode 'stops' when it is encased with less than 2" of concrete.Originally posted by georgestolz:
]Is the #4 CU the grounding electrode, or the Grounding Electrode Conductor to the electrode?
What that does not say is that the connection shall be required to be encased.Exception: An encased or buried connection to a concrete-encased, driven, or buried grounding electrode shall not be required to be accessible.
The point of connection is irrelevant.Originally posted by georgestolz:
Around here, the Ufer is allowed to protrude from the foundation for the connection of the GEC.
See 250.68(A):
What that does not say is that the connection shall be required to be encased.Exception: An encased or buried connection to a concrete-encased, driven, or buried grounding electrode shall not be required to be accessible.
That is comparing apples to oranges.Originally posted by georgestolz:
Comparing the Ufer to the water pipe,
Or simplified.A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing effectively bonded to the pipe) and electrically continuous (or made electrically continuous by bonding around insulating joints or insulating pipe) to the points of connection of the grounding electrode conductor and the bonding conductors.
Originally posted by iwire:
George I am sorry we are butting heads so much lately.
A concrete encased electrode is a highly similar concept to water pipe. A water pipe is a dirt-encased electrode.