Re: Ground Conductor Splicing
George, if you don't mind...
I'll pass on the UFER discussion for now.
George, if you don't mind...
I would use the wording: "The area under "Required Connection" is the portion of the electrode that we are required to bond for, not to, if we wish this pipe to qualify as an electrode.Originally posted by georgestolz:
Part 1. The area under "Required Connection" is the portion of the electrode that we are required to bond to, per the definition detailed in the first sentence of 250.52(A)(1).
No, to use the piping as an electrode, this is where we're required to make the connection. It is discussed in code.Part 2. The area under the "?" is not discussed in code. It is commonly perceived that we may connect our GEC in this location, but it is not expressly permitted.
Again, bonding anywhere on the piping is permitted, but not if we wish the piping to do sevre as an electrode.Part 3. The area under "Mandatory: No Connection" is expressly forbidden for GEC connections, by the second sentence of 250.52(A)(1).
I'll pass on the UFER discussion for now.