Re: Ground Conductor Splicing
Originally posted by charlie b:
Originally posted by iwire: If it does not end where I think it does, where would you or George say it ends?
I think the electrode certainly ends at the point you connect a GEC to it.
I can't agree with this statement. Perhaps I'm misunderstanding what you're saying.
IMO, the electrode continues until it doesn't resemble an electrode anymore. Otherwise interconnecting electrodes would be impossible: because as soon as a GEC was connected, you'd be outside of the electrode when you came along with the next conductor.
IMO:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">In the case of a water pipe, it is an electrode until it switches to PVC, or ends in a sink. (If this were not the case, we wouldn't need to be prohibited from attaching near the sink.)</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">In the case of structural metal, it ends at the ends of the structure.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">In the case of a Ufer, it ends at the end of the #4 or rebar.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">In the case of a ground ring, it ends...it uh...well it ends...is this a polish joke?</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">In the case of a rod, it ends at the end of the rod.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">In the case of a plate, it ends at the end of the plate.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
I'm opening this up a tad, because of this statement:
How far can I 'stub out' the rebar before I must connect to it?
Can I stub out and run a 100' across the building to the service by tying steel rebar together?
Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means.
What would the support and physical protection requirements be for this string of rebar?
Here in the real world, we can surmise that the steel tie wires are a temporary fastening means to secure rebar together until such a time that the concrete is poured, and the concrete creates the permanent structural bond for the rebar (for our purposes).
For the purposes of the NEC, I believe they are clarifying that the surface contact of rebar pressing against rebar, brought about by lashing pieces of rebar together, is sufficient. Using clamps and conductors to connect the different pieces of rebar is not necessary.
With that in mind, lashing pieces of rebar together with steel tie wires would not be very permanent outside of the concrete.
250.68(B) Effective Grounding Path. The connection of a grounding electrode conductor or bonding jumper to a grounding electrode shall be made in a manner that will ensure a permanent and effective grounding path.
While this is talking about the actual connection of the GEC to the electrode, I think it stands to reason that if that connection must be permanent and effective, then so should the electrode it's hooked to.
A solid piece of rebar, or a solid piece of #4, is not going to disintegrate in short order. A metallic water pipe is not going to disintegrate. The top of a ground rod isn't going to disintegrate. The, uh...well the ground ring's fine too.