- Windsor, CO NEC: 2023
- Hospital Master Electrician
Re: Ground Conductor Splicing
Bob, I had a hum-dinger of a response written up, and then She Who Must Be Obeyed booted me off and lost it.
Edit on last cut: This post wound up twice as long, sorry.
2. It says that you cannot use beyond 5' as part of the GES.
There's a subtle difference between these two concepts that is pivotal to our discussion. One, although the interior does not qualify as a grounding electrode, they assume we will make our connection to the electrode from the interior. This is profound. This makes my case. This sets a precedent that there is no specific permission to use portions of this particular object, that are connected to but not qualifying as "electrode", but it is inherently allowed.
It is inherently allowed because they have to write language to restrict it. Working backward, if this sentence did not exist, then we could do exactly what it's prohibiting us from. Otherwise it's existence would be pointless.
The presence of the "shall not be used" comment indicates that if this sentence weren't there, I could run my GEC to the toilet next to the service. I could connect anywhere in the structure, so long as the pipe were "continuous to the points of connection of the grounding electrode conductor and the bonding conductors."
The 5' comment is not in the description of the electrode. It's a peripheral rule related to the pipe, but it's not a descriptor of the pipe itself.
As electricians, a water pipe electrode is second nature to us, because it's easy, and it's always done a certain way. You never install your own, it usually looks the same, we never have to give it much thought.
Then again, for many, it's also natural to look to the water pipe as a "primary" grounding electrode. It's natural for someone to assume they must install a "secondary" ground rod for a Ufer. They did it for a water pipe. People operating on their daily experiences without research will rely on their experience to come to their own conclusions. You have taught me and dispelled some of these myths for me.
It's natural to look at a piece of #4 and call it a "conductor." It's not natural to look at that same item protruding from a concrete wall and call it an "electrode." If it were a chunk of rebar, it'd be an easier pill to swallow. As it is, it just doesn't feel right.
Recently I posted a series of methods that a local inspection agency listed as being acceptable. I just searched high and low for it, but it appears the thread (or just my post) was deleted. It was long and I'm not going to re-type it. I don't believe that I said anything inflammatory, and I don't remember the tone being tense when I left the thread, so I'm a little ticked it was deleted.
For the "preconceptions" portion of our discussion, it was a fine display of how a chunk of rebar sticking out is more acceptable to our collective tastes than the #4 version of what the NEC considers to be the exact same thing.
Can you point to the differences that you think are the most relevant?Originally posted by iwire:
George the wording describing a water pipe grounding electrode and a concrete encased electrode are quite different.
Let's look at it.A water pipe grounding electrode can and does exist outside of the ground up to 5'.
1. It does not say that the electrode is 5' long once it's inside.Interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall not be used as a part of the grounding electrode system...
You took the words right out of my mouth.Read the sections carefully using "Charlie's Rules".
Forget what you have done or what you think they should mean.