xformer
- Dallas, Tx
- Master Electrician
Does the code require the grounded conductor be brought to the first means of disconnect on a separately Derived System?
The first paragraph of 250.30 does not include 250.24 in the list of other articles that apply, so I say no.
If the grounded conductor from a separately derived system (i.e. transformer) is not included with service conductors a ground fault has no path back to the Xfmr XO (or corner grounded delta) -- until it goes phase to phase.
You can bond the grounded conductor in the transformer.
why ? if its not neededOf course, but the grounded conductor also has to be routed with the secondary conductors to the CB or fused switch.
I agree with Action Dave. The neutral is not required to be brought to the disconnect, but a supply side bonding jumper is required from the transformer to the disconnect. See 250.30(A)(2)
I agree also, you would only need to bring it to the disconnect if that is where you're installing the system bonding jumper.
I believe you need to bring the SSBJ to the disconnect no matter where the system bonding jumper is installed.
agree, The supply-side bonding jumper would be needed to bond the transformer and disconnect regardless of the location of the system bonding jumper but the grounded conductor only needs to be routed to the location of the system bonding jumperI believe you need to bring the SSBJ to the disconnect no matter where the system bonding jumper is installed.
It could be a metallic raceway. Also how does that impact the need to bring in the grounded conductor?
The SSBJ could be a non-flexible metallic raceway. The grounded conductor only needs to be brought to the disconnect if that is where you choose to install the system bonding jumper, or you are serving neutral loads.
Agreed, I think I said part of that in post #11.![]()
Agreed. But if its not bonded to the windings you'll need the grounded conductor as well, this is the only way the service CB will trip upon ground fault.