Hey, I never read (2017) 250.30 closely before yesterday. But for the case of a grounded SDS with wye secondary that serves only line-to-line loads, it is clear to me that there are a few different ways to provide a fault clearing path between the transformer and the disconnect:
A) Use an SBJ at the transformer only. In which case there must be an SSBJ from the transformer to the disconnect. No grounded conductor is required between the transformer and the disconnect. If one were run, it would not connect to anything in the disconnect, it would just sit isolated from the metal enclosure and any other conductors.
B) If the transformer is in the same building as the disconnect, use an SBJ at the disconnect only. In which case there must be both an SSBJ and a grounded conductor from the transformer to the disconnect.
C) If the transformer is not in the same building as the disconnect, use SBJs at both the transformer and the disconnect. In which case there must be no SSBJ run between the transformer and the disconnect, but there must be a grounded conductor.
The difference between (A) and (C) in this case seems primarily semantic. E.g. for an existing installation under (A) with the transformer outdoors, no continuous metallic conduit, and an SSBJ of the wire type, I could cut the SSBJ in the disconnect and splice the two ends back together. Then the portion of the former SSBJ coming from the transformer I could recolor white and call the grounded conductor, and the other portion I could call the SBJ, and now the installation fits (C).
Cheers, Wayne
A) Use an SBJ at the transformer only. In which case there must be an SSBJ from the transformer to the disconnect. No grounded conductor is required between the transformer and the disconnect. If one were run, it would not connect to anything in the disconnect, it would just sit isolated from the metal enclosure and any other conductors.
B) If the transformer is in the same building as the disconnect, use an SBJ at the disconnect only. In which case there must be both an SSBJ and a grounded conductor from the transformer to the disconnect.
C) If the transformer is not in the same building as the disconnect, use SBJs at both the transformer and the disconnect. In which case there must be no SSBJ run between the transformer and the disconnect, but there must be a grounded conductor.
The difference between (A) and (C) in this case seems primarily semantic. E.g. for an existing installation under (A) with the transformer outdoors, no continuous metallic conduit, and an SSBJ of the wire type, I could cut the SSBJ in the disconnect and splice the two ends back together. Then the portion of the former SSBJ coming from the transformer I could recolor white and call the grounded conductor, and the other portion I could call the SBJ, and now the installation fits (C).
Cheers, Wayne