JohnJ0906
- Baltimore, MD
stickboy1375 said:roger said:Stickboy, what state are you in, and what does this inspector use as back up to his not allowing a 4 wire feeder to an out building?
If there are any conductive parallel paths between these buildings he is causing a potentially dangerous scenario and a NEC violation.
"He may be in for bigger problems in 2008 if the three wire allowance is prohibited."
Not really since AHJ has the final say... :>
I live in connecticut, I don't see the problem, why would you want a fault to travel all the way back to the original service? I think the state electrical inspector and our power supplier, (Connecticut Light & Power) require this install... for example, if I installed a 200a pedastal service I would have a meter with 200a main breaker combo, drive 2 ground rods, bond the neutral to the ground rods, Then pull 3 wires to the house, install a 200a main breaker panel, drive 2 ground rods, again bond the neutral to the ground rods... Bond water etc... call it done... I do the same when I do a remote pool panel also...
This sounds like a violation to me. If the Main breaker i.e. the main service disconnect is outside I would have to pull 4 wires to the house (2 hots, neutral, ground) and NOT bond ground and neutral inside- its a subpanel. I would also have to bond the water to the MAIN, not the panel. I am refering to the example above (200amp pedistal servive) not the original question