Uh, the whole reason for the supplementary electrode is that the NEC assumes that we can't look at one end and the other and assume it's an electrode. It could have a plastic repair beside the house.IMO if you look at the water meter out at the street and the pipe inside - and both are copper - and it's an older install - one could assume it's copper. And need to be treated as an electrode. Leaving you to take it through, over, under or around the house...
There is no depth requirement for a GEC. You can install it at 2" if you like, if it's deemed to be not exposed to physical damage.if you like you can attach it to the house.
actually i am not sure of the depth, i know it is not 24" or 18" for that matter. that is why it has to be sized as a #4 because it can withstand physical damage.
if someone knows can they post it or give a code referrance.
if you like you can attach it to the house.
actually i am not sure of the depth, i know it is not 24" or 18" for that matter. that is why it has to be sized as a #4 because it can withstand physical damage.
if someone knows can they post it or give a code referrance.
IMO if you look at the water meter out at the street and the pipe inside - and both are copper - and it's an older install - one could assume it's copper. And need to be treated as an electrode. Leaving you to take it through, over, under or around the house...
Uh, the whole reason for the supplementary electrode is that the NEC assumes that we can't look at one end and the other and assume it's an electrode. It could have a plastic repair beside the house.
I'd say that the OP tell the HO that the EI approved the installation as it sits for good reason, there is little benefit to going to extremes to get within 5' in these circumstances. The two ground rods are good enough.
I'd hate to think of the electrical inspector as disinterested.Yes, I intend to do that, once I have talked to the inspector, and confirmed that he has no objections. Perhaps he can re-assure them as a dis-interested party.
I'd hate to think of the electrical inspector as disinterested.![]()
![]()
There is no depth requirement for a GEC. You can install it at 2" if you like, if it's deemed to be not exposed to physical damage.
However, if that assumption is a false one, depending on an electrode that isn't one could be an issue, too.IMO if you look at the water meter out at the street and the pipe inside - and both are copper - and it's an older install - one could assume it's copper. And need to be treated as an electrode.
However, if that assumption is a false one, depending on an electrode that isn't one could be an issue, too.
If an inspector can say "Unless you expose 10' of pipe for me to see, we can't assume it's an electrode," so can we.
I believe it's less hazardous to be wrong treating it like it's not an electrode than being wrong treating it as one.
The shortest pathway between the electrical system bonding point and the metallic water system is the best pathway.
If an inspector can say "Unless you expose 10' of pipe for me to see, we can't assume it's an electrode," so can we.
Agreed, and as RW said in post 16, you'll be happy to install anything beyond NEC requirements he wants to pay extra for.I'd say that the OP tell the HO that the EI approved the installation as it sits for good reason, there is little benefit to going to extremes to get within 5' in these circumstances. The two ground rods are good enough.
Thanx, Bob! You're too kind.I agree with Larry's thoughts here particularly this one.
I had been trying to find a way to word that very thought.![]()
You're too kind.![]()
Thanx, Bob! You're too kind.![]()
You're right. I'm sorry. I don't know what I was thinking. :roll:Now that is just a bold faces lie and I will not tolerate such accusations. :grin:
What I should have said is, "Bob, you never have anything nice to say about anyone!"![]()
Eat my shorts!Danke![]()
Ok guys, show a little restraint the OP is back! Just kidding. Anyway, thanks for the support for a fellow contractor, in the face of the evil home owner. These guys bought the house from somone else, went 50-50 for cost of the heavy up. Some details of their transion went a little south, and the new owner is venting at my expense, or at least that's my impression of it.
It's okay; my comment is electrical in nature:Ok guys, show a little restraint the OP is back! Just kidding.
Shorts are electrical.Eat my shorts!![]()