Inspector's view:
You installed a 200A service with 2 ground rods.
Only a #6 copper needs to be run to the rods which are your electrodes.
The water pipe is now not an "electrode" and needs a #4 copper to bond it. It can be bonded at any point.
If you want to call your water pipe that is underground and verified to have 10' underground an electrode (why would you at this point) then you have to make your GEC connection within 5' of the entrance of the metallic water pipe.
Sounds like you are good to go if you simply bond the H20 with #4 at the nearest convenient point.
You installed a 200A service with 2 ground rods.
Only a #6 copper needs to be run to the rods which are your electrodes.
The water pipe is now not an "electrode" and needs a #4 copper to bond it. It can be bonded at any point.
If you want to call your water pipe that is underground and verified to have 10' underground an electrode (why would you at this point) then you have to make your GEC connection within 5' of the entrance of the metallic water pipe.
Sounds like you are good to go if you simply bond the H20 with #4 at the nearest convenient point.